So am I right in saying when I use a socket for a kettle the current is going from the mains through the LH RCD to the MCB to the kettle and the return current is then going down the neutral back through the LH RCD (all ok at this point) up to the neutral bar where the RH RCD neutral is also connected, but because there is a N to E fault in a circuit that side the current is instead flowing down the RH RCD neutral to the earth somewhere which then trips the RCD as there was a imbalance (due to no live current being drawn that side)
Yes, that's the general idea, but there might also be a balanced current flowing through the RH RCD as well, if the RH circuits are in use. May be 30A flowing through the live of the RH RCD, but if there's 30.02A flowing through the neutral of the same RCD, even for just a few milliseconds, then off it goes.
 
Yes, that's the general idea, but there might also be a balanced current flowing through the RH RCD as well, if the RH circuits are in use. May be 30A flowing through the live of the RH RCD, but if there's 30.02A flowing through the neutral of the same RCD, even for just a few milliseconds, then off it goes.
But instead of the lighting current returning form the circuit down its neutral the sockets neutral current is going the other way trying to get to earth through the failt
 
As I explained earlier, there is a parallel path for the neutral current to return to the service head. One that results in a small proportion of the neutral current from the socket circuits, but not the live current, flowing through the RH RCD, thus unbalancing it.
The proportion of diverted current is the ratio of the resistance of the neutral tail compared to the resistance of the RH circuit neutral, fault resistance, RH circuit cpc, and main cpc, which can be a very small proportion, BUT 20mA is a very small current, when compared to the many tens of amps that can flow as an inrush current on the socket circuits.
Would this be the case for the other lighting circuits tho because they all work fine and don't trip the RCD. Surely any current would try to use the parallel path to earth from the faulty neutral. How come the other lighting circuits are ok and work okay
 
But instead of the lighting current returning form the circuit down its neutral the sockets neutral current is going the other way trying to get to earth through the failt

All depends on the resistance of the actual fault. If it's low enough, then the lighting circuits may well trip their RCD.
Did a continuing test at the CU. Got a positive reading from neutral to earth on the right hand side. Disconnected neutrals and investigated more, found a lighting circuit with the fault. Just need to try and actually find where iit is. So far I've looked into 3 switches, and one ceiling rose and one bathroom fan. All seem ok . More hunting needed.
 
Outside lights are often the culprit
As said before.
 
Outside lights are often the culprit
As said before.
Unlikely on this circuit. There is a outside light but I've split the circuit before it and still getting the fault. It's either in the toilet or dining room. Suspected the extractor fan but seems ok.

Split the circuit at the dining room switch for the down lights. So the issue actually must be in the bathroom seeing as the dining room down lights no longer connected to neutral.
 
Unlikely on this circuit. There is a outside light but I've split the circuit before it and still getting the fault. It's either in the toilet or dining room. Suspected the extractor fan but seems ok.

Split the circuit at the dining room switch for the down lights. So the issue actually must be in the bathroom seeing as the dining room down lights no longer connected to neutral.
Have the light switches got a Neutral in them ?
 
You said the fault was on a lighting circuit and the Alarm panel is a spur off the ring final ??.

An alarm bell box is unlikely to have a mains supply to it, as already said.
Alarm panel is on a spur. The bell box i suspect is wired into the lighting circuit. Would explain that when I set the alarm of the fault began. Probably caused a short as the bell box is obviously outside.
 
Alarm panel is on a spur. The bell box i suspect is wired into the lighting circuit. Would explain that when I set the alarm of the fault began. Probably caused a short as the bell box is obviously outside.
A bell box will be powered by 12v and will also have an internal battery.
If there is a mains supply to this bell box it, will either have an internal transformer or will have one inline.

It's highly unlikely that the bell box would be giving an N to E fault, it probably doesn't even have an earth.
 

Reply to RCD issue baffling me in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
239
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
255
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
348

Similar threads

My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
317
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
698

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top