RCD issue, or is it? | on ElectriciansForums
Discuss RCD issue, or is it? in the UK Electrical Forum area at ElectriciansForums.net
the pict
Mentor
Brodick
Changed a consumer unit everything fine all test came back hunky dory, but one RCD would not trip on the test button so swapped them around, same deal,I then got random trips from unassociated circuits IE kitchen ring plug in kettle and the opposite RCD would trip disconnect incoming earth RCD,s behave normally Ze .18 didn't clamp the earth to check any current flow did't think of it till on my way back, the only other thing I did after the tests was connect an outside light for the tenant to existing cable, so i am thinking a shared N any clues would be great
Dev
I think you have mis read my OP,
I don't think it's that the OP has been misread, than the fact you've explicitly stated you're going to be disconnecting CPCs with the assumption you will be re-energising (otherwise how would you be able to see that RCDs are behaving).
so my plan is to disconnect the earths one by one to get the RCD to behave and hopefully indentify the culprit
An I-R test will almost certainly find this fault. My money would be a N-E fault, hence why only higher loads are causing issues.
As someone who's managed to get 'trusted advisor' status on here, this is a little worrying then you're just disconnecting things randomly.
Like I said done that and all test come back ok, but, and this is the bit that aint playing ball with every circuit without anything plugged in, cooker,shower immerse etc etc all disconnected and all bulbs out and in the switched on position doing a global IR I get a X reconnected everything I get random trips, dis main earth random goes away
Thats because you assume I am some sort of idiot
Reply to RCD issue, or is it? in the UK Electrical Forum area at ElectriciansForums.net
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...