Changed a consumer unit everything fine all test came back hunky dory, but one RCD would not trip on the test button so swapped them around, same deal,I then got random trips from unassociated circuits IE kitchen ring plug in kettle and the opposite RCD would trip disconnect incoming earth RCD,s behave normally Ze .18 didn't clamp the earth to check any current flow did't think of it till on my way back, the only other thing I did after the tests was connect an outside light for the tenant to existing cable, so i am thinking a shared N any clues would be great
Dev
 
I think you have mis read my OP,

I don't think it's that the OP has been misread, than the fact you've explicitly stated you're going to be disconnecting CPCs with the assumption you will be re-energising (otherwise how would you be able to see that RCDs are behaving).

so my plan is to disconnect the earths one by one to get the RCD to behave and hopefully indentify the culprit
 
An I-R test will almost certainly find this fault. My money would be a N-E fault, hence why only higher loads are causing issues.

As someone who's managed to get 'trusted advisor' status on here, this is a little worrying then you're just disconnecting things randomly.
 
Like I said done that and all test come back ok, but, and this is the bit that aint playing ball with every circuit without anything plugged in, cooker,shower immerse etc etc all disconnected and all bulbs out and in the switched on position doing a global IR I get a X reconnected everything I get random trips, dis main earth random goes away
 
An I-R test will almost certainly find this fault. My money would be a N-E fault, hence why only higher loads are causing issues.

As someone who's managed to get 'trusted advisor' status on here, this is a little worrying then you're just disconnecting things randomly.
Thats because you assume I am some sort of idiot
 

Reply to RCD issue, or is it? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
738
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
693

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top