Changed a consumer unit everything fine all test came back hunky dory, but one RCD would not trip on the test button so swapped them around, same deal,I then got random trips from unassociated circuits IE kitchen ring plug in kettle and the opposite RCD would trip disconnect incoming earth RCD,s behave normally Ze .18 didn't clamp the earth to check any current flow did't think of it till on my way back, the only other thing I did after the tests was connect an outside light for the tenant to existing cable, so i am thinking a shared N any clues would be great
Dev
 
Disconnecting a cpc when there is a known fault to earth could raise the earthed parts of that circuit (or if you disconnect the main earth, then all exposed and extraneous parts) up to the line voltage which is not a safe thing to do.
I would recommend that if your IR tests are coming back OK and you cannot find the fault by dead testing that you disconnect a circuit entirely (i.e. at least line and neutral) to remove it from the installation. Then if you put a high powered load on another circuit and the RCD does not trip you have disconnected the faulty circuit and can start checking that one in detail.

In this way if a faulty circuit is still present the RCD will limit the risk.
 
Mud slinging aside, if you've done the dead tests in the correct order, you should of discovered the fault before the live tests. Once on a rewire, I discovered a neutral earth fault on a radial and decided to put it to one side for later, to get the other circuits on. Except I didn't and mixed it up with another radial and connected it up. Got to RCD test and wouldn't function, neither would RCD test button. Went back to basics, and discovered my mistake.

Happy hunting:)
 
Have you got an earth clamp meter?

I think you need to check the residual earth loss across the installation and I suspect you have a combination of a N-E fault and cumulative earth leakage from plugged in devices....
 
Yeah sometimes you just don't want to hear the stuff thats already rattling around in yer head

Remember to tell us what the problem is/was when you find it.
I had one (intermittent tripping) last week, three hours it took to discover an external light switch buried in decking, soaking with condensation. Methodical often wins the day!
 
A neutral earth fault can prevent the RCD test button tripping the RCD, see my and others previous posts. Don't ask me why, I'm not that clever, others might have the technical reason. From personal experience, but once experienced, its something you remember.
 
In the end it was a new LED hall light I put in before I took the old board out to give my self light to work as there was none there to begin with, I rigged it up from the henly blocks all kosher via a temp fcu,and it was the last thing into the board and this was causing the issue, as I said my plan was to remove the earths in turn till the tripping stopped and it was the culprit, what' the saying assume nothing suspect everything, well I assumed "cos its new it's ok" , all circuits test out great and as it is class 2 I disconnected the earth till scewjobs send a new one, cheers all for insisting I had a N..E fault
Pict
 

Reply to RCD issue, or is it? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
738
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
693

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top