Rcd issues | on ElectriciansForums

Discuss Rcd issues in the UK Electrical Forum area at ElectriciansForums.net

A

Andyg4

Hi new to the forum, but got a feeling I may be on here quite a bit. I recently had to do a board Change at work due to the RCDs on the split load board not meeting the disconnection times. With all circuits put away across the 2 sides of the board and all in the off/open position I energised the board to do the basic mechanical test on the RCDs, ie the test buttons. The 1st one closest to the supply tales serving breakers 1 to 5 operated fine and when tested 1x and 5x was fine and within the times. The 2nd RCD serving breakers 6 to 10 would not operate by the test button and would not disconnect in time when 1x and 5x tested. I swapped the RCDs over to prove a faulty RCD but with no joy as the 1st one now in the 2nd ones place didn't operate on the test button or within the times and the 2nd one in the 1st ones place operated fine within the times and on the test button. although the test buttons don't operate the RCDs trip approx 5 mins after being on with no load on at all. I'm left scratching my head a bit on this one. The only thing I keep thinking of is a possible neutral earth fault somewhere? Any suggestions would gratefully received. Cheers
 
its obviously not wired up correctly, id guess that you've got the neutral for rcd 2 in the wrong bar.

How is that obvious?

A much safer bet would be that there is a certain type of fault on one of the circuits which causes this behaviour. A fault which will show up of dead testing is carried out correctly
 
How is that obvious?

A much safer bet would be that there is a certain type of fault on one of the circuits which causes this behaviour. A fault which will show up of dead testing is carried out correctly
seen it before. a N-E fault not necessarily on the same RCD can c ause this.
 
Well dave he swapped the board because of suspected faulty rcds. He's put a new board in and one rcd doesn't work, it's not the rcd because he's tried it on the other side and it works. So as there were no faults before and the rcd isn't broken so it makes it obvious that it's not wired up correctly.
 
Well dave he swapped the board because of suspected faulty rcds. He's put a new board in and one rcd doesn't work, it's not the rcd because he's tried it on the other side and it works. So as there were no faults before and the rcd isn't broken so it makes it obvious that it's not wired up correctly.

How do you know there were no faults before? All we know is the previous board had suspected faulty RCDs, and that he jumped to the conclusion that the RCD must be faulty when thus board behaved unexpectedly.

This is the same story we get every couple if weeks on here when an inexperienced person with minimal training carries out a CU change on an installation with an existing N-E fault.
 
Hi new to the forum, but got a feeling I may be on here quite a bit. I recently had to do a board Change at work due to the RCDs on the split load board not meeting the disconnection times. With all circuits put away across the 2 sides of the board and all in the off/open position I energised the board to do the basic mechanical test on the RCDs, ie the test buttons. The 1st one closest to the supply tales serving breakers 1 to 5 operated fine and when tested 1x and 5x was fine and within the times. The 2nd RCD serving breakers 6 to 10 would not operate by the test button and would not disconnect in time when 1x and 5x tested. I swapped the RCDs over to prove a faulty RCD but with no joy as the 1st one now in the 2nd ones place didn't operate on the test button or within the times and the 2nd one in the 1st ones place operated fine within the times and on the test button. although the test buttons don't operate the RCDs trip approx 5 mins after being on with no load on at all. I'm left scratching my head a bit on this one. The only thing I keep thinking of is a possible neutral earth fault somewhere? Any suggestions would gratefully received. Cheers

Well why not test for one then?....
 

Reply to Rcd issues in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
698
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
745

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top