Hello
What a day. I have just changed an old rewireable consumer unit for a new shiney twin RCD unit but the sockets are tripping the RCD. When all the appliances are unplugged the RCD stays in. When I plug some appliances in it is okay. When I plug other appliances in it trips. The RCD ramp test indicates it is tripping at 27ma. The ring has continuity on all each of the conductors. I've done an insulation resistance test on 250V on line to earth and have 240Mohms but seem to be getting 0 Mohms on Neutral to Earth. The circuit breaker is staying in.
Really appreciate any ideas as to why this RCD could be tripping.

Thanks
 
If your measuring 0 MOhms N-E, then you need do a continuity test on the ring between N-E. You will probably find a resistance of several tens of KOhms or greater, this is causing the N-E leakage path, but the resistance is high enough not to trip the RCD directly, however, as the appliances are connected the leakage increases until a point is reached which trips the RCD.
Once you have identified the problem, further continuity tests around the ring should find the point of the fault.
 
Hello
What a day. I have just changed an old rewireable consumer unit for a new shiney twin RCD unit but the sockets are tripping the RCD. When all the appliances are unplugged the RCD stays in. When I plug some appliances in it is okay. When I plug other appliances in it trips. The RCD ramp test indicates it is tripping at 27ma. The ring has continuity on all each of the conductors. I've done an insulation resistance test on 250V on line to earth and have 240Mohms but seem to be getting 0 Mohms on Neutral to Earth. The circuit breaker is staying in.
Really appreciate any ideas as to why this RCD could be tripping.

Thanks

Eliminate the actual socket accessories, switch them all to the off position, I have a a problem of Low I/R where two sockets caused high resistance problems of 40Meg when the socket was switched on but oc when in the off position. This problem as you can guess can come and go dependent on switch positions. See the photo..

[ElectriciansForums.net] RCD keeps tripping on socket circuit

IR should be at 500V but I guess your only running 250V until you clear the fault... and remove the conductors from the consumer unit common bars so you are sure you are only testing your circuit concerned.

Have you done all your dead tests (end to ends to make sure you have a ring etc)?

To trouble shoot find the mid point and do 50/50 split i/r tests to see where the issue is.
 
Thanks for all your help.

No sooner unfortunately. I've arranged a work around for them so they're happy enough. The chap has done a fair bit of his own wiring I think so he's being quite reasonable.
 
I changed a board and 2weeks later I got a call RCD was tripping sourced it to a faulty iron and the customer said but thats the top of the range and cost me ÂŁ65 2 years ago I tested on my PAT tester and it failed so in your case you need to pin it down to what appliance or at what socket it is tripping
 
Just a quick one. Might sound like a silly question but as I'm getting 0 Mohms on a N-E insulation resistance test, why isn't the circuit breaker tripping when the circuit is energised?
 

Reply to RCD keeps tripping on socket circuit in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

Similar threads

M
  • Question
I believe you're in Australia? Could you clarify the distribution arrangements - is this RCD for one particular circuit, or is it protecting a...
Replies
1
Views
195
Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
496

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top