RCD keeps tripping on socket circuit | Page 2 | on ElectriciansForums

Discuss RCD keeps tripping on socket circuit in the Australia area at ElectriciansForums.net

GPack

-
Joined
Jun 30, 2009
Messages
192
Reaction score
1
Hello
What a day. I have just changed an old rewireable consumer unit for a new shiney twin RCD unit but the sockets are tripping the RCD. When all the appliances are unplugged the RCD stays in. When I plug some appliances in it is okay. When I plug other appliances in it trips. The RCD ramp test indicates it is tripping at 27ma. The ring has continuity on all each of the conductors. I've done an insulation resistance test on 250V on line to earth and have 240Mohms but seem to be getting 0 Mohms on Neutral to Earth. The circuit breaker is staying in.
Really appreciate any ideas as to why this RCD could be tripping.

Thanks
 
Switch your meter over to Ohms after the IR test and find out what it is reading.

The RCD will detect a earth neutral imbalance but if the ohms reading is over 7666 ohms the RCD will most likely hold.

230/0.03 = 7660.

Now when you find what it is reading you will have to start spliting the cct to find the problem as its well under 1Meg from your IR test !
 
Another thing to remember, is that with TN-C-S, the earth and neutral are connected at the head.
Only way to see if there is continuity between the earth and neutral in the installation, is to ensure the neutral is disconnected.
You need the main switch off, not just the MCB.
 

Reply to RCD keeps tripping on socket circuit in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

Similar threads

M
  • Question
I believe you're in Australia? Could you clarify the distribution arrangements - is this RCD for one particular circuit, or is it protecting a...
Replies
1
Views
195
Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
496

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top