The sunbeds will have lots of filters in them each leak to earth. Fit rcbos, and if the customer wonders about the extra cost then explain if a bed goes faulty then he will only have an issue with 1/4 of his beds not all 4.
You’d think the OP would of thought about that rather than closing a whole shop down because of one faulty device.
 
That is the whole point of this thread. The LEDs don't suppose to have anything to do with the sunbeds but they DO.

EVERY time the LEDs are off, the beds trip an incomer RCD.
EVERY time the LEDs are on, the beds work fine.

LEDs are in the separate consumer unit and are not connected to the distribution board incomer.

Yes. I do have a copy of the regs.
 
Next time don't give the customer the option.

They are running as business ... Hours lost cost far more than a couple of rcbo's

Best get back on site and use your tester
 
You are absolutely right about not giving a customer an option in this case.

I will be there next week and try to get an earth leakage metre too. They are not cheap but seem very useful.
 
It's costing me a lot cause the place is 100 miles away. Only agreed to do it because the owner is a friend of a friend. Big mistake.
 
The clamp is a must,on issues such as this,but if the only thing i had was a screwdriver,i would be pulling the neutral on that mcb switched lighting circuit,and seeing what happened...
 

Reply to RCD / LED problem in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
706
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Update. Went back today as it was popping the other RCD post move, again intermittently with no real pattern. Typically overnight but not every...
Replies
6
Views
277
Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
793

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top