do rcds give low readings when testing insulation resistance
Discuss rcd low insulation resistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
If they have a white fly lead which you have'nt disconnected, or if you are testing L-N with it closed
Sorry to be picky but a "white fly lead" is only found on RCBO's, not RCD's.
I've got a couple of MEM 61008 RCDs, both have fly leads.....
Agreed, I haven't seen many for the 61008 RCDs with earth reference fly leads.
remove fly lead from neutral bars. test from L busbar 1 to N 1 with breakers on, RCD off. repeat for L2 busbar and N2. as this is a L-N test, all loads will need removing proir to testing.