Hi looking a little help. Replaced a consumer unit in a house with a contactum 8way dual rcd split board. After finishing it I tested with rcd tester at 1 time and 5 times with the rcd tripping in correct times. I went to connect up boiler after with the cable dead I cut it but the rcd would not trip. Then at the db I linked out the earth bar and neutral bar and neither rcd tripped to try and see if it would anyone any ideas?
 
If you cut the wire after a double pole fused spur the only cable connected back to the fuse board is the earth, therefore no fault will be seen by the RCD

Edit: Sorry , Sedgy34 beat me to it
 
i think people get mixed up with "if the circuit is dead" and "if the RCD is dead"....if the circuit is dead..but the RCD is still energised....then it will still sense a N-E fault on the dead circuit.....but if the RCD is dead....then of course it wont sense any faults on the circuit/s it feeds.....
 
i think people get mixed up with "if the circuit is dead" and "if the RCD is dead"....if the circuit is dead..but the RCD is still energised....then it will still sense a N-E fault on the dead circuit.....but if the RCD is dead....then of course it wont sense any faults on the circuit/s it feeds.....
Is it a faulty rcd then if so why would the tester still give good tripping times
 

Reply to Rcd not triping in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
791
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
962
  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
631

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top