A F1 for further investigation myself I was going to put a C3 and state RCD does not operate within the trip times and place no more than 12 months till next test property is in the middle of house sale thanks
It's a Hager board RCD circuits are sockets up and down and shower. TNCS earthing tested at a socket there is nothing on as House is empty but MCBs where all on
Il put it down as C2 I am going back to test at the RCD itself with loads disconnected and see what happens, iv megger the all circuits and no issues on low readings. When I tested it at socket 1 times came up 300ms so that's why I done Ramp test. I suspected it was a faulty RCD. Thanks for your help guys
Sorry, I just assumed (obviously incorrectly) that you had carried out the test properly in the first place.
Don't code anything until you have carried out the test correctly and then think about coding it.
Why would you suspect a faulty RCD from an incorrectly carried out test? You might as well IR test a socket circuit with appliances plugged in and conclude that a cable has degraded from a low reading!!
me and geordie are old, bu tnot faulty. senile perhaps.
the recommended test interval is 10years for domestic but can be less if you feel that it is required.
The switch is held in mechanically, so in my opinion I would have tested the trip a few times before doing a final check, then act accordingly.
Then the label is a waste of time, but I do take your point.The problem with doing that is that someone isn't going to press the Test button half a dozen times before every earth fault.
Then the label is a waste of time, but I do take your point.