Hi,
One of my electricians came across a fault today which we cannot fathom out.
New split load (dual RCD) board fitted, all insulation and continuity and earth loop readings are ok.
When testing the RCD's at 1/2 ,1 and 5 times at 180 degrees the test is as normal, i.e 1/2 no trip, 1 and 5 times it trips within 40ms.
However at 0 degrees the RCD does not trip at all.

This happens on BOTH RCDS, we though we cant be that unlucky with 2 faulty RCDs, but they were changed and it still does the same.

Is this a supply fault - contact the DNO????

ANY ideas????
 
Have you tried the test kit on a known good RCD, or have you tried a different tester on the suspect RCD`s. I agree highly unlikely to have 2 duff ones. I can see no reason why the RCd only trips at 180' its only a coil and should trip which ever direction it is energised.
It has to be your tools..pardon the pun.
Cheers....Howard
 
Last edited by a moderator:
Have you tried the test kit on a known good RCD, or have you tried a different tester on the suspect RCD`s. I agree highly unlikely to have 2 duff ones. I can see no reason why the RCd only trips at 180' its only a coil and should trip which ever direction it is energised.

Cheers....Howard

Thanks, as its a long distance job - not yet. However the unit was only calibrated in November but I know this doesnt mean much in the real world.
 
Have you tried the test kit on a known good RCD, or have you tried a different tester on the suspect RCD`s. I agree highly unlikely to have 2 duff ones. I can see no reason why the RCd only trips at 180' its only a coil and should trip which ever direction it is energised.
It has to be your tools..pardon the pun.
Cheers....Howard

It has been known for parts to be manufactured and found that batches to be defective and later recalled
 
I fitted a wylex cu in march the RCD was defective cost me in time and head scratching and replacement.I just could not believe a new cu was defective.Also fitted a wylex rcbo on a circuit at anorther job,that then had nuisance tripping faults so fitted a new rcbo,same tripping,then wired circuit via rcd protected circuit and has been fine since.Tested two rcds in 10way board last week one had ramp test of 25ma the 2nd rcd was 15ma which seems a bit low to me,and why the big difference
 
Last edited by a moderator:
I know this is an old post but I have had the same issue today. The property in question has two consumer units. Testing one RCD on Board 1 all tests work as they should @1/2, 1, 5 on both 0 and 180 degrees.

The RCD in board 2 will not trip at 1x on 0 degrees but will at 5x and does for 1x and 5x at 180 degrees.
I have replaces the RCD 3 times all with the same results,3 different makes of RCD. Ramp test comes back with >51

I k now my tester is working fine, and other suggestions ?
 
I know this is an old post but I have had the same issue today. The property in question has two consumer units. Testing one RCD on Board 1 all tests work as they should @1/2, 1, 5 on both 0 and 180 degrees.

The RCD in board 2 will not trip at 1x on 0 degrees but will at 5x and does for 1x and 5x at 180 degrees.
I have replaces the RCD 3 times all with the same results,3 different makes of RCD. Ramp test comes back with >51

I k now my tester is working fine, and other suggestions ?
Are you testing at the RCD with all loads isolated? Are there any ballast or other such devices on the circuits fed by the RCD?
 

Reply to RCD not tripping at 0 Degrees in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
328
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
390
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
687
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top