explain ramp test for me please
RCD's generally trip anywhere between 50% and 100% of their nominal rated current it is common and perfectly normal for a 30mA RCD to trip between 15mA and 30mA but on average in the low twenties of mA.
On most RCD testers with a ramp function, when you press the test button, the tester progressively increases (ramps up) the circuit leakage current in 1mA steps, until such time as the RCD trips, you can then read the display which gives the value of current in mA at which the trip occurred.
When ramp testing, if there is already an existing leak on the circuit this can reduce the reading further as the existing leak will just add to the meter ramp effect giving a false early trip value.
If their is no existing leakage on the circuit, then a reading less than 15mA is likely to be prone to nuisance tripping and you should consider replacing the RCD.
This test, like all RCD tests, should be carried out directly at the RCD load side (output) terminals with the final circuit disconnected or at least with all loads removed.