Hi

Hopefully some can explain this perplexing issue

I'll try and explain the situation as best I can, hopefully its not to rambling -maybe its common knowledge but I'll bow to anyones supperior understanding



During an EICR checked test button RCD would not trip - checked with tester no trip on X1 or X5 so informed client it was faulty

Split load board 5 ways non RCD 2 ways RCD Hager Ze 0.20

however please refer to my very bad drawing attached.

Later on in testing - I switch off MCB A and rcd trips try to reset it cant do this unless MCB C is switched off then RCD will reset
MCB C put off RCD trips immediately

Live test with RCD off there is a feed C to A at top of MCB

Tested RCD with loads disconnected - functions perfectly.


There is an interlink between circuits A and C - kitchen was wired by clients friend who altered circuits and has obviously mixed up fixed appliance ring with downstairs ring.

Although I am getting continuity between all 4 ends - was hoping to solve problem by making 1 big ring but this is not possible.

Having to go back and try and sort this mess - its a house sale that concludes 4 weeks buyer want EICR seller is client.

Not looking forward to fault finding - all tiled etc may have to consolidate all A and C cables into 1 20A mcb but very reluctant to do this as putting problem onto someone else


So - if all the above is clear can anyone explain why this interconnection between RCD protected circuits prevents and RCD from functioning?

Obviously there is a lesson for me to initially check an RCD that doesn't function with the loads disconnected in future

Many thanks

[ElectriciansForums.net] RCD not tripping - tech advice
 
The rcd is not faulty if it functions with all protective devices in the off position. If the rcd circuits and non rcd circuits are interconnected then this problem would have been evident to the client prior to your EICR because the rcd just would not have stayed on.
 
Is there a possibility of an appliance fault that is leaking dc into the circuit? This can lock the rcd and prevent it functioning.
 
Hi thanks for all replies

IR L-N L-E N-E all > 199 Mohms

Client was unaware of fault as RCD stays on as long as mcb C is on
everything runs as it should apart from RCD test button doesn't trip

Neutrals may have been interconnected from non RCD side to RCD side at circuit wiring, but by this point I had spent an extra couple of hours on job trying to suss this out and lost the will.

I don't think the "kitchen fitter" was sophisticated enough to come up with a convoluted plan to prevent RCD tripping, as no wiring was altered in CU

I left the job with circuits A and C both connected onto mcb A with neutrals onto RCD bar.

The RCD function properly so assuming no N-E faults as RCD performing as should.

Still cant get my head round why this interconnect would stop RCD from tripping?, If I had the patience I would set it up on a bench to see if I could replicate circumstances. Any further ideas?

Unfortunately I've take responsibility for this now, it would have been great just to ID faults issue EICR and walk away for someone else to fix. I hate testing sometimes....

I am going back this week to try and work out whats going on but am only going to spend an hour on it - could spend all day - as lifting floors and cutting holes in plasterboard not an option.

How would you feel about putting circuits A and C onto 1 20A mcb?
usual kitchen appliances and living room sockets. As I said before I'm not comfortable with it, but it is a solution. Also what do I put on EICR knowing what I know if this is done?

Many thanks again
 
Ok, next thought is the circuit controlled by MCB C is bypassing the RCD. So no trip. With MCB C off it removes its L but leaves N which provides an extra path for current from MCB A circuit to trip RCD.

Hi thanks,
this kind of makes a bit sense to me but not being a fault finding expert still cant quite get my head round it.

I have spent many frustrating hours trying to get my head round apparently simple faults.

IR tests were done with circuits disconnected, MS is DP

As a further solution I will try and separate into 2x 20a radials at some point in botched circuit(s)and run off spare RCD way.

Many thanks to all for your thoughts and inputs, I appreciate the help and advice, especially as its non critical as to ones knowledge and skills
 
I’d see wether it’s possible to convert the 2 rfc into 1 at the ccu and put onto a 32a, making sure the appropriate neutrals are in the correct neutral bar

Hi

thanks, as I mentioned earlier, making both into 1 RFc was my first choice, however I was getting continuity at all 4 ends( lives) so not possible.
Client has lifted floor up above today and sent me some pics of a few choc box joints, so I've got a good place to start to see whats going on.

Still can get my head round initial circumstances of non tripping.
 

Reply to RCD not tripping - tech advice in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
864

Similar threads

Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
498
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
685

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top