Hi
Hopefully some can explain this perplexing issue
I'll try and explain the situation as best I can, hopefully its not to rambling -maybe its common knowledge but I'll bow to anyones supperior understanding
During an EICR checked test button RCD would not trip - checked with tester no trip on X1 or X5 so informed client it was faulty
Split load board 5 ways non RCD 2 ways RCD Hager Ze 0.20
however please refer to my very bad drawing attached.
Later on in testing - I switch off MCB A and rcd trips try to reset it cant do this unless MCB C is switched off then RCD will reset
MCB C put off RCD trips immediately
Live test with RCD off there is a feed C to A at top of MCB
Tested RCD with loads disconnected - functions perfectly.
There is an interlink between circuits A and C - kitchen was wired by clients friend who altered circuits and has obviously mixed up fixed appliance ring with downstairs ring.
Although I am getting continuity between all 4 ends - was hoping to solve problem by making 1 big ring but this is not possible.
Having to go back and try and sort this mess - its a house sale that concludes 4 weeks buyer want EICR seller is client.
Not looking forward to fault finding - all tiled etc may have to consolidate all A and C cables into 1 20A mcb but very reluctant to do this as putting problem onto someone else
So - if all the above is clear can anyone explain why this interconnection between RCD protected circuits prevents and RCD from functioning?
Obviously there is a lesson for me to initially check an RCD that doesn't function with the loads disconnected in future
Many thanks
Hopefully some can explain this perplexing issue
I'll try and explain the situation as best I can, hopefully its not to rambling -maybe its common knowledge but I'll bow to anyones supperior understanding
During an EICR checked test button RCD would not trip - checked with tester no trip on X1 or X5 so informed client it was faulty
Split load board 5 ways non RCD 2 ways RCD Hager Ze 0.20
however please refer to my very bad drawing attached.
Later on in testing - I switch off MCB A and rcd trips try to reset it cant do this unless MCB C is switched off then RCD will reset
MCB C put off RCD trips immediately
Live test with RCD off there is a feed C to A at top of MCB
Tested RCD with loads disconnected - functions perfectly.
There is an interlink between circuits A and C - kitchen was wired by clients friend who altered circuits and has obviously mixed up fixed appliance ring with downstairs ring.
Although I am getting continuity between all 4 ends - was hoping to solve problem by making 1 big ring but this is not possible.
Having to go back and try and sort this mess - its a house sale that concludes 4 weeks buyer want EICR seller is client.
Not looking forward to fault finding - all tiled etc may have to consolidate all A and C cables into 1 20A mcb but very reluctant to do this as putting problem onto someone else
So - if all the above is clear can anyone explain why this interconnection between RCD protected circuits prevents and RCD from functioning?
Obviously there is a lesson for me to initially check an RCD that doesn't function with the loads disconnected in future
Many thanks