Been to a job today where the customer is saying thier RCD is randomly tripping, TT system new job all wired 6 months ago ZE 0.70 ( Cracking TT ZE) Earth loops and ins res test all fine, But the RCD wont trip when tested with my tester , Started with a ramp test no trip, auto tested all 6 tests no trip at 1x or 5x rcd . Oddly the other rcd on the other curuicts is fine, replaced rcd with new same issue wont trip but does manual trip with button , now im confused it may be something simple i missing. It's a crabtree star breaker 30/30 set up.

Any Ideas ?
 
Tested at the RCD with all loads removed?
 
but have you tried testing at the RCD itself with all the relevant MCBs OFF?
 
then i would think that it's either incorrect wiring or you got a couple of dodgy RCDs. try swapping them round tom see if the one that works on the other side trips in place of the one that doesn't. if so, it's deffo the RCD at fault.
 
Had the same thing before on an a new BG board, it turned out the neutrals were the wrong way round. But as this board has been in and working for a few months I doubt it's that.

All cable terminations within the board OK?
 
loose connection on RCD tails?????? check the manufacturers connections as well.
 
Are you sure your connections are correct. When you test at socket & it works, i presume youre using a plug in lead with an MFT,etc. if Im not mistaken the meter needs the earth to make the test work....so...."using inference & deduction my dear Holmes" Im guessing your green lead isnt connected to a reliable earth and therefore it isnt working (the RCD test).


Just a guess, don't quote me
 
Istalled a new RCd unit from the wholesaler , can't swap the other its different , im thinking the boards been adapted some how, im sure the installs not been done by a spark well not a registed one but all the conections leads etc look right and the earths fine as mentioned at the start.
 
Tel, yes, but just thinking if main earth is disconn'd somewhere for example, leads might be ok looking at them but ... Dunno.


Is that 0.70 a true Ze of just the earth rod or with parallel paths still connected?
 
[ElectriciansForums.net] Rcd not tripping when tested ?
Originally Posted by telectrix [ElectriciansForums.net] Rcd not tripping when tested ?
but have you tried testing at the RCD itself with all the relevant MCBs OFF?



Yes Done this to


TT Ze of 0.7
Something not adding up there

Are the insulation resistance values ok
Were the outgoing neutrals also disconected for the rcd test?


 
[ElectriciansForums.net] Rcd not tripping when tested ?
Originally Posted by telectrix [ElectriciansForums.net] Rcd not tripping when tested ?
but have you tried testing at the RCD itself with all the relevant MCBs OFF?






TT Ze of 0.7
Something not adding up there

Are the insulation resistance values ok
Were the outgoing neutrals also disconected for the rcd test?



See im baffled by the ze yes water and gas bond disconected Defo tt even got a note on the cut out dont supply PME ,16mm to 3/8 spike at source then a 16mm 3 core swa via a switch fuse to the DB, i never disconected outgoing neutrals on my rcd test at the unit its self , the testers only 3 months old but im hearing there are issues with the earth pins inside it's a robin MFT going to borrow a mates and see if thats the issue, but i just can't understand one working and the other not. Looking in the board im not 100% its not been adapted from a old 100amp 30/ma split load style and the busbars etc might not be right but it all seemed to be conected fine to me. A longer look maybe required apon my return i think.
 

Reply to Rcd not tripping when tested ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
687
davesparks
D
I don’t see an rcd here. Is it elsewhere, supplying this board? It looks like it’s in a garage… is there excessive moisture getting into...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top