Hi all

I'm stubbed on a new installation which I tested today. It is a M2 split board with a TT earthing system. All test results were fine until I attempted RCD tests. The test button works on both RCD's and the RCD main switch. The main switch is 0.1A and the two RCD's is 0.03A. But they both don't trip when 1x and 5x is attempted on my Fluke. It is a small installation so I checked everything and there is screws etc through anything and the polarity of the RCD is fine.
I haven't changed the RCDs yet as wondering if anyone else has come across this and may know anything else I could check.

Thanks
 
Are you testing the RCDs at the load terminals with outgoing cables disconnected, or with the tester connected to a circuit?

What is the Ra?
 
This is the other query as the figure I got was 412 ohms which I believed was to high (200 ohms)but my boss stated it was fine and within 1665 ohms which is acceptable.
 
How many rods and how deep?

I don't know the soil conditions where you are so can't comment on that value without a bit more information. If you've achieved that with multiple long rods then it will probably be stable, or if it's just one little rod then it is unacceptable.

That is a very high Ra but it should not prevent the RCD operating.
Test the RCDs with the outgoing conductors disconnected and see how it goes.
 
I have had a couple of instances with Ra's around 500-600 ohms where the RCD would trip, but not in the permitted times. Both these installs were upgraded to PME and the trip times were then satisfactory. Agree with DS; if it's one four foot rod only then it will likely be unstable and fluctuate markedly.
 
Last edited:
I will give that a go tomorrow thanks. It is just one small rod so I will mention to the big man for a longer or multiple rods.
 

Reply to RCD not tripping in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
813

Similar threads

Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
496
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
654

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top