ive been called to a caravan where the power keeps tripping out. ive got a 30ma rcd, which feeds a db with main switch, zs of 16.6 and all circuits clear. when i drop the 10mm tails off the load side of the rcd and test on x1 im getting >40 and x5 >400. and >51mA. ive tried 2 new rcd's and all the same. however with the tails reonnected and test done at a socket im getting >40 x1 and 19 x5 and 46mA.

what is going on?

thanks
 
What make of RCD is it? Some don't like being tested on the outgoing terminals.

Think that only applies to MEM units, and even then, you only need to attach a few inches of conductor to them and test from the ends of those conductors. All the other manufacturers recommend testing at the units terminals.
 
look...if its taking 51mA on ramp..then what do you think?
have you got the tester set correctly?

- - - Updated - - -

do you know how to test...
answer truthfully as if you arn`t sure..we can give some guidance here....
 
I do but any extra guidance would be appreciated. A 30 mA rcd should trip less than 30 not greater. X1 less than 200 and x5 less than 40. Testing the rcd on load side with no load it want trip on x1 but will on x5 and ramp test is giving >51 hence no trip on times x1. So why is this the third rcd same problem
 

Reply to rcd not tripping in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
414
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Yea all out circuits were disconnected & Rcd ramped tested Think this will be the right way forward,with EL clamp meter Cheers have a nice Christmas 😎
Replies
2
Views
1K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
961

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top