I have been out to a nuisance tripping RCD this morning, there are 3 socket circuits, 1 boiler circuit, and 1 oven circuit protected by the RCD.

I started by checking the IR between L-E and N-E, the reading was between 2 and 3 M ohms on every circuit and leg.

I then disconnected the CPCs for each circuit in turn and I was still getting between 2 and 3 M ohms between L and the earth bar.

I disconnected all the CPCs and was getting varying readings between the lives and CPCs of the other circuits.

I was also getting varying voltages between the L and CPC's even when the RCD was turned off.

I was also getting various voltages between the different CPCs

Can anyone explain what would cause this?

Cheers
 
I have been out to a nuisance tripping RCD this morning, there are 3 socket circuits, 1 boiler circuit, and 1 oven circuit protected by the RCD.

I started by checking the IR between L-E and N-E, the reading was between 2 and 3 M ohms on every circuit and leg.

I then disconnected the CPCs for each circuit in turn and I was still getting between 2 and 3 M ohms between L and the earth bar.

I disconnected all the CPCs and was getting varying readings between the lives and CPCs of the other circuits.

I was also getting varying voltages between the L and CPC's even when the RCD was turned off.

I was also getting various voltages between the different CPCs

Can anyone explain what would cause this?

Cheers
Have you done any tests on the RCD or checked what leakage currents are present
 
I disconnected all the CPCs and was getting varying readings between the lives and CPCs of the other circuits.

Hi - fwiw, I think these various voltages are induced. The proximity of the floating conductor to an L will induce a voltage in the floating conductor. This is normal and it’s reason to tie all unused conductors to ground.
 

Reply to RCD nuisance tripping headscratcher. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
395
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
980
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Induced voltage can be a bit of a red herring when using DVM my guess is somethings moist.
Replies
5
Views
469
TerryBNZ
T
  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
870

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top