I have been out to a nuisance tripping RCD this morning, there are 3 socket circuits, 1 boiler circuit, and 1 oven circuit protected by the RCD.

I started by checking the IR between L-E and N-E, the reading was between 2 and 3 M ohms on every circuit and leg.

I then disconnected the CPCs for each circuit in turn and I was still getting between 2 and 3 M ohms between L and the earth bar.

I disconnected all the CPCs and was getting varying readings between the lives and CPCs of the other circuits.

I was also getting varying voltages between the L and CPC's even when the RCD was turned off.

I was also getting various voltages between the different CPCs

Can anyone explain what would cause this?

Cheers
 
I have been out to a nuisance tripping RCD this morning, there are 3 socket circuits, 1 boiler circuit, and 1 oven circuit protected by the RCD.

I started by checking the IR between L-E and N-E, the reading was between 2 and 3 M ohms on every circuit and leg.

I then disconnected the CPCs for each circuit in turn and I was still getting between 2 and 3 M ohms between L and the earth bar.

I disconnected all the CPCs and was getting varying readings between the lives and CPCs of the other circuits.

I was also getting varying voltages between the L and CPC's even when the RCD was turned off.

I was also getting various voltages between the different CPCs

Can anyone explain what would cause this?

Cheers
Have you done any tests on the RCD or checked what leakage currents are present
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Leeds

Thread Information

Title
RCD nuisance tripping headscratcher.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6
Unsolved
--

Advert

Thread statistics

Created
dtec dave,
Last reply from
Wilko,
Replies
6
Views
962

Advert

Back
Top