L
loz2754
Thanks. So where is it then? I see no attachment.I've given an example just as you posted this ? it's from a design project
Thanks. So where is it then? I see no attachment.I've given an example just as you posted this ? it's from a design project
So the risk assessment would have to include some sort of mitigation to prevent use of the dedicated socket outlets for other purposes, especially if used to supply mobile equipment outdoors.I understand that side of things however the original design is only for the welding equipment, there are other outlets for other devices and all other tools used in the bays are either air tools or battery tools.
Thanks.
Thank you i will see if I can use this.Thanks.
Interesting and useful but not really a risk assessment for justifying omission of RCDs for additional protection.
This unfortunately is the side of the job I’m trying to learn, I’ve spent my entire working life on the tools and not much time on the paperwork side of things, unfortunately also I have no one to turn to in our office for advice and help, hence why ive posted to the forum. Hoping someone would maybe have a suitable scenario that they have been through themselves.Interesting and useful but not really a risk assessment for justifying omission of RCDs for additional protection.
A risk assessment should identify the hazards, who or what is at risk and from what? And then should identify what has been put in place to minimise the danger presented by such hazards.
The format was dictated by city and guilds so I can't really comment beyond that. It justifies omission with appropriate reg numbers, outside of the regs I'm not entirely sure what you'd want on it.Interesting and useful but not really a risk assessment for justifying omission of RCDs for additional protection.
A risk assessment should identify the hazards, who or what is at risk and from what? And then should identify what has been put in place to minimise the danger presented by such hazards.
All I see is a somewhat useful list of where RCDs may or may not be required by BS7671, not a justification where it may be desired or necessary to deliberately omit an RCD in a situation where it would normally be required.The format was dictated by city and guilds so I can't really comment beyond that. It justifies omission with appropriate reg numbers, outside of the regs I'm not entirely sure what you'd want on it.
The point of it is we're justifying omission using the regs to present the argument.
By all means take it up with C&G, I merely offered it as an example, you're welcome to expand on it or devise one to share.All I see is a somewhat useful list of where RCDs may or may not be required by BS7671, not a justification where it may be desired or necessary to deliberately omit an RCD in a situation where it would normally be required.
You're welcomeThank you so much for your help,
Is there a published document listing the reasons that socket outlets require RCDs?Interesting and useful but not really a risk assessment for justifying omission of RCDs for additional protection.
A risk assessment should identify the hazards, who or what is at risk and from what? And then should identify what has been put in place to minimise the danger presented by such hazards.
Tempting as it is, it never really works to think in terms of the regulations themselves when considering the risks.I struggle to see what dangers are introduced by the bit of wire from each machine terminating in a plug+socket instead of fixed connections.
How can some regular bozo be expected to carry out a risk assessment permitting him (or her!) to contravene the laws set by a panel of experts without knowing their reasoning?
Why is a new DB required? Surely this is just a recommendation at worst for that scenario?I'm on an EICR for a bakery with a dozen+ 32a 3ph sockets feeding large fixed floor standing machines of various functions and ages. The place runs 20+ hours a day and the 32a seems to be a standard presumably so they can be swapped out promptly. New DB reauired.
In this sort of scenario I really doubt the lack of RCD protection for those sockets represents anything more than a C3 code, so no need to replace the DB.I'm on an EICR for a bakery with a dozen+ 32a 3ph sockets feeding large fixed floor standing machines of various functions and ages. The place runs 20+ hours a day and the 32a seems to be a standard presumably so they can be swapped out promptly. New DB reauired.
That's a great observation. And once again regulatory obligations and market options diverging.Just a thought ...
Does there exist a plug/socket similar to BS4343 (Commando) but with two earth pins ?
Seems to me that (for this discussion) the primary requirement is as backup for failed earthing. Similar to RFCs where high leakage currents are expected require high integrity earthing, having duplicated earth paths would go a long way to mitigating the risks.
Some of that style of plug can be reversed (the ones with the twin side earths) and others cant (the ones with the earth pin) but typically most now accept either.From what I've observed doesn't the German schumo socket have dual earth contacts? Although they can be reversed too so it might be for that reason.
But it's still one contact, one cable core, one connection inside the equipment - so while it does mitigate one particular failure mode, it doesn't mitigate several others.... more likely the integrity of the CPC connection to the pin and that is where the larger BS4343 (Commando) plugs benefit from having dual screws for retaining the cables.
True.But it's still one contact, one cable core, one connection inside the equipment - so while it does mitigate one particular failure mode, it doesn't mitigate several others.
That sort of situation is what I normally deal with and most equipment has multiple earth paths via cables and metal racks, plus I normally bond the rack as well as the supply cable CPC so two paths at least.Back to one of the earlier situations - telecoms facilities. I would suggest that these are relatively simple - there's options for bonding everything so if (say) a supply cord loses the CPC, there's still bonding so ADS will still work without anything exposing dangerous voltages. Plus it's a relatively controlled environment - the operator has the option of ensuring only properly trained people go in. I'd have no problem doing an RA and specifying additional bonding (if not already present) for every item, plus training of all personnel who enter the facility.
This might be the reason for the "electrically skilled" aspect not listed, so stuff like that is picked up by anyone with even basic PAT experience.But for some of the others mentioned (factories, bakeries) it's a lot harder. My limited experience in commercial environments is that people are happy to ignore any warning notices or instructions if they get in the way of doing their job. Plus people seem happy to carry on using equipment with obvious faults. For example, one time I was in the local hospital (visiting) I observed someone happily trundling along with a heated food trolly, where the cable gland was something like 6" away from the hole it was supposed to be fitted into, and presumably it was only the electrical connections of the cores keeping the cable in - i.e. it was a really obvious fault, visible from a distance, and not some obscure issue that could have been overlooked (I told the person trundling it that it was dangerous and needed referring to maintenance before it was used again - no idea if it was). I'm sure we've all got tales like that - especially cables pulled out of cord grips/glands. And the least said about some of the stuff we used to do back when I was a youngster working on a local farm - before I knew any better.
The issue is then you need dual CPC to the equipment, etc, and that is very unlikely to be supported. You could tie some 4mm flex in parallel with the power cord and fit at any chassis screw, etc., but I can't see that as being acceptable in general. More generally, if equipment is seriously abused as you see on farms and building sites, both could be visibly damaged an nobody cares!So I'd be "rather wary" of omitting RCD protection for some of these situations unless there was some sort of unique plug/socket arrangement that offered a bit more protection than a standard BS4343 or BS1363 type - hence my query about connectors with multiple earth pins.
Replace the 3 (or 5) core cable with 4 (or 6) core, find an alternative internal connection point.The issue is then you need dual CPC to the equipment, etc, and that is very unlikely to be supported. You could tie some 4mm flex in parallel with the power cord and fit at any chassis screw, etc., but I can't see that as being acceptable in general.
Absolutely. I do wonder how some of us survived - or perhaps it was wearing wellies that helped.More generally, if equipment is seriously abused as you see on farms and building sites, both could be visibly damaged an nobody cares!