What does the 18th say about RCD on commercial lighting
Discuss RCD on commercial lighting in the Lighting Forum area at ElectriciansForums.net
Only in domestic dwellings.Thought all lighting had to have RCD protection now
Can’t find any reference in the 18th to separate commercial from domestic on lightingOnly in domestic dwellings.
Thought all lighting had to have RCD protection now
Probably not if its not a regulation, thats why I said I thought they all had to be RCD'd and not it was a fact.Why do you think that? Can you support this with a regulation?
Has that changed from any of the previous books, I'm sure I read a regulation somewhere that simply said all lighting has to be RCD'd now. Having said that I was absolutely sure that a socket couldn't go within 3M of a bath and even every google result says the same yet it's now 2.5M in the latest book. They do like to fiddle about.Have a look at 411.3.4 in the book
Has that changed from any of the previous books, I'm sure I read a regulation somewhere that simply said all lighting has to be RCD'd now. Having said that I was absolutely sure that a socket couldn't go within 3M of a bath and even every google result says the same yet it's now 2.5M in the latest book. They do like to fiddle about.