RCD or Not | on ElectriciansForums

Discuss RCD or Not in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

telectrix

-
Mentor
Nearly Esteemed
Arms
Joined
Sep 5, 2010
Messages
73,534
Reaction score
71,830
Location
cheshire/staffordshire
Just been called out to install cooker circuit. 6mm and 45A Isolator Switch, obviously dedicated circuit. Existing Wylex D/B with 1 Ring for whole house on RCBO, 2 Lighting not RCD. 1 Spare way with 16A MCB, assume was for Immersion Heater, no longer used. Changed 16A MCB for 32A and connected cooker cable to this. My query is ___ should I put RCBO instead as the new circuit is all surface, no buried cables, only a 3m run in cupboard under stairs, thtough studded wall into kitchen surface clipped under kitchen unit to Isolator, then to Connection Unit behind cooker. The problem with fitting RCBO is that it won't fit as the neutral bar is just above the MCBs and would stop the RCBO fitting on the DIN Rail. I have adviseed the client that the D/B should be upgraded.
 
Assuming there is no socket outlet on the isolation switch,and u can verify no buried cables,(that is all cables in trunking etc),then u are half way there..however the disconnection time on that circuit still has to be met without the rcd,..and if its a tt system it wont be!
 
that's what i thought. i get R1+R2 of 0.02 and Zs reading of 0.30. seems ok to me.
 

Reply to RCD or Not in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K
  • Question
This charger doesn't support rear entry from the looks, only bottom entry, hence that. Unless they make a white sheathed SWA, I would still need...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top