Found the issue!!!

The kitchen sockets were run as spurs from spurs from spurs etc!! it turns out the feed from the kitchen comes from one socket upstairs that then went into a JB in the ceiling of the kitchen Extension and then splits into 2 radials. None of the cables fused down. There was a leak in the roof of the extension which was causing the JB to get wet thus giving me the fruity readings and tripping the RCD

I ended up Isolating the circuit from the socket which cleared the fault. The Oven and Hob are fed from different circuits each with their own isolator and socket and there is a computer socket in the kitchen that is on another circuit not on the RCD side of the board. so she still has some power in the kitchen that she can plug fridge into etc. I have advised my sister that the house needs a rewire to get rid of all the dodgy circuits but she cant afford one right now so things will stay as they are.

Thanks for all your help guys!

Dave
 
Last edited:
If it's affecting all 3 conductors it sounds like a JB which is wet or a choc block buried in plaster. Like Handyspark says use the low res ohmmeter. Could even be mice chewing through the PVC under the boards.
 
If it's affecting all 3 conductors it sounds like a JB which is wet or a choc block buried in plaster. Like Handyspark says use the low res ohmmeter. Could even be mice chewing through the PVC under the boards.

Mate: Read the thread, he's already found & sorted the problem. lol
 

Reply to RCD Problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
295
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
277
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
354

Similar threads

  • Question
Yea all out circuits were disconnected & Rcd ramped tested Think this will be the right way forward,with EL clamp meter Cheers have a nice Christmas 😎
Replies
2
Views
1K
  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
831

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

  • exceeding voltage drop
    The cable is way undersized. If the voltage drop is detrimental to the installation I would make...
  • TT advise
    OK My take on the precautions to implement when omitting an up front RCD on a TT system. Tails...
  • SIL vs ATEX
    Good morning all, I have a question for those who are CompEx and SIL aware - I have various Ex...
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top