rcd problems please help | on ElectriciansForums
Discuss rcd problems please help in the UK Electrical Forum area at ElectriciansForums.net
demkap
hi there i need a bit of help basically the rcd trips and the shower mcb trips the same time. then its ok for a day then it randomly does it during the night etc even when the shower isnt in use, any ideas?
Have you done an IR test to start with, if the mcb trips when there is no load on the circuit i can only assume there is a problem with the mains incoming side of the shower causing the short!
nope i will do though but it doesnt trip everytime... flicked breaker and rcd back up and then was ok but the next morning the rcd and shower mcb tripped.
- - - Updated - - -
its weird that the mcb trips aswell that would mean theres a overload i believe?
it would seem to be that shower circuit wouldnt it if its the only that keeps tripping guys? how about i do some tests on it r1 + r2 and zs tests?
wander lead out....method 2 on it...
and IR as well...
thats on the cable....if its clear then move on to the shower....IR cold....then warm it up...and IR again...
Reply to rcd problems please help in the UK Electrical Forum area at ElectriciansForums.net
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
davesparks