Rcd problems | Page 2 | on ElectriciansForums

Discuss Rcd problems in the Australia area at ElectriciansForums.net

Joined
Feb 7, 2009
Messages
360
Reaction score
16
Location
.
Following the addition of a socket to a ring circuit I have just carried out the RCD trip test with a Fluke tester.
The RCD would not trip on x 1 or x 5. Then tried the test button on the RCD and it would still not trip even with all the circuits turned off.
On closer inspection found that the line conductor to the RCD was connected at the base along with the bus bar (bypassing RCD) also found a link had been added between the two neutral bars.
After speaking to the customer it transpires that on fitting of a new kitchen the electrician also convinced them a new consumer unit was required (no reason not to believe that) However, after fitting the split load unit the RCD constantly tripped on all socket circuits ( x 4 ). Customer was advised too much leakage and the RCD was bridged to allow power to all circuits.

What is the best way to go about putting this right to give RCD protection.
 
Almost sounds as if you don't have both ends of the rings correctly identified. Is it possible that RFC1 out and RFC2 in are paired and RFC1 in and RFC2 out are paired, not necessarily by you ;)

Edit:
You may only be looking for one fault if that's the case.
 
Last edited:
Almost sounds as if you don't have both ends of the rings correctly identified. Is it possible that RFC1 out and RFC2 in are paired and RFC1 in and RFC2 out are paired, not necessarily by you ;)

Edit:
You may only be looking for one fault if that's the case.

My thoughts exactly. As I now intend to do the basic ring and insulation tests etc I will find if thats the case.

Will let you all know what the result was. Cheers
 
Hi all, Update on this thread is that following ring tests on these circuits I found the following :-

On three of the four circuits tested all was ok and good insulation test results.
However, on the fourth circuit, three wires were present.
The three line conductors into the MCB were two on a ring and the third on a radial. The radial was only 2.5 t/e on the 32 MCB and had 4 2g sockets and 1 3g socket on it. Corrective action on this part not yet done.
The other two which were on the ring failed insulation test on cpc to neutral so when RCD wired correctly fault was neutral to earth bar so all circuits tripped RCD. I split the offending ring at various points to narrow down the problem to two seperate faults. First was a damaged cable under the downstairs kitchen floor trapped under a replaced floorboard. I replaced that length of cable. The second fault was between a junction box under the kitchen floor and two sockets hidden with newly installed kitchen units. Unable to get to the one of the two sockets i ran a new cablefrom under floor to next used socket and by passed the two hidden which were unusable anyway. could have been fault in socket or screw from kitchen unit fixings in cable who knows but problem solved. RCD then wired correctly in consumer unit and all works fine. Testing complete and satisfactory. Now to correct the radial, no spare way to run from a 16A and no obvious way to access cables other than at consumer unit as yet.
 
Thanks for the update always nice to know how things turn out. Well done on identification and rectification, hope someone does not try to reconnect the bypassed sockets! Good luck with sorting the radial, sound like it is a bit of a practical problem there.
 
Thanks for the update always nice to know how things turn out. Well done on identification and rectification, hope someone does not try to reconnect the bypassed sockets! Good luck with sorting the radial, sound like it is a bit of a practical problem there.

Cheers. Cut both the cables to the hidden socket under the floor very close to the boards so no chance of access to socket or cables unless kitchen comes out.
 

Reply to Rcd problems in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
145
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
952
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
2K
Ok I’ll try this when I’m down
Replies
4
Views
490

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top