Following the addition of a socket to a ring circuit I have just carried out the RCD trip test with a Fluke tester.
The RCD would not trip on x 1 or x 5. Then tried the test button on the RCD and it would still not trip even with all the circuits turned off.
On closer inspection found that the line conductor to the RCD was connected at the base along with the bus bar (bypassing RCD) also found a link had been added between the two neutral bars.
After speaking to the customer it transpires that on fitting of a new kitchen the electrician also convinced them a new consumer unit was required (no reason not to believe that) However, after fitting the split load unit the RCD constantly tripped on all socket circuits ( x 4 ). Customer was advised too much leakage and the RCD was bridged to allow power to all circuits.
What is the best way to go about putting this right to give RCD protection.
The RCD would not trip on x 1 or x 5. Then tried the test button on the RCD and it would still not trip even with all the circuits turned off.
On closer inspection found that the line conductor to the RCD was connected at the base along with the bus bar (bypassing RCD) also found a link had been added between the two neutral bars.
After speaking to the customer it transpires that on fitting of a new kitchen the electrician also convinced them a new consumer unit was required (no reason not to believe that) However, after fitting the split load unit the RCD constantly tripped on all socket circuits ( x 4 ). Customer was advised too much leakage and the RCD was bridged to allow power to all circuits.
What is the best way to go about putting this right to give RCD protection.