fixit4u

HI ALL,
ANYONE SHED SOME LIGHT ( PARDON THE PUN ) ON RCD PROTECTION FOR BATHROOM CIRCUITS DOMESTIC/HOTELS ETC FOR PERIODIC TESTING,AS I WAS UNDER THE IMPRESSION THAT ALL BATHROOM CIRCUITS REQUIRE RCD PROTECTION !
THERE SEEMS TO BE A BIG DEBATE AT MY WORK AS IF THIS APPLIES TO BATHROOMS IF THE PIPES,LIGHTS,SHAVER POINTS ETC ARE BONDED WITH > 2.5MM CABLE THAT THIS DOES NOT APPLY ? OR THE ONLY CIRCUIT IN THERE IS LOW VOLTAGE LIGHTING ?BUT HAVE FOUND NO REF TO THIS ANYWHERE,THE COMPANY HAS TRIED TO PUT AN END TO THIS DEBATE FINALLY AS WE ARE ALL GETTING A BIT ****** OFF WITH IT AND PHONED THE NIC TWICE TO BE TOLD NO RCD IS NOT REQUIRED AND THEN YES THAT IT DOES ON ALL BATHROOM CIRCUITS ?

ANY HELP PLEASE !!!!!!!! :confused:
 
It is required on all circuits within a bath/shower room....supplementary bonding may be ommited if RCD protection is in place and other conditions are met....If a PIR is being carried out on a pre-17th install lack of RCD protection to a bath/shower room would be a code 4.....The relevant regs are in section 7 of the BRB...701.411.3.3....701.415.2
 
Agree with code 4.
If you ring the helpline and say "are rcd's required on all bathroom circuits then, quite correctly, the answer is 'yes'.

The reg's are not retrospective so that's why the code 4 is applied.
 

Reply to rcd protection-bathrooms in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
814

Similar threads

Usually if there are only C3 observations it would usually be deemed satisfactory but could be found to be unsatisfactory in unusual...
Replies
15
Views
2K
davesparks
D
No to all. Also would require a means of isolation for PIV - pulling a fuse wouldn't be acceptable. I don't mean to seem disrespectful, but this...
Replies
1
Views
1K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top