I'm sure this will have been covered before but please bear with me. Have been asked to replace a main Distribution board for a fairly small caravan site and add in some new hook ups ( space for 8 x 16A sockets currently but upgrading to 12 x 16A and a 32A).

Now this is all fed from one 100A 1361 type 2 supply which i have made client aware might struggle to cope as there is already a small shower block fed from here also... alas he would like to go ahead all the same.

Anyway basically all hook up points have there own RCBOs for each socket and the shower block an RCD in its sub main board. Can the supplies from the main DB to the hook ups and shower block just be connected to Mcbs and a 100A Main switch stop to nuisance tripping or do these supplies also have to be Rcd protected. Swa cables are all buried and will be earthed at mains end.

Thanks folks.
 
Not sure of the caravan park license terms nowadays, but when I was on the site, we had 50 touring pitches, and the toilets were the minimum we needed… 2 showers, 5 cubicles and maybe 5/6 basins per ladies or gents.
Also 1 disabled shower/ wc room.
 
Not sure of the caravan park license terms nowadays, but when I was on the site, we had 50 touring pitches, and the toilets were the minimum we needed… 2 showers, 5 cubicles and maybe 5/6 basins per ladies or gents.
Also 1 disabled shower/ wc room.
What's required and what's desirable aren't necessarily the same thing. If I rocked up on a touring site and found two showers for 50 pitches, then I don't think I'd stay long or be back
 
What's required and what's desirable aren't necessarily the same thing. If I rocked up on a touring site and found two showers for 50 pitches, then I don't think I'd stay long or be back
Likewise.

I meant 2 in ladies, 2 in gents…. And they have showers in touring caravans now, so it’s half expected you use your own.

It’s funny that when I go to a site, I find the toilet blocks hardly used… never busy…. But when we ran a site, it was like Piccadilly Circus.
 
Likewise.

I meant 2 in ladies, 2 in gents…. And they have showers in touring caravans now, so it’s half expected you use your own.

It’s funny that when I go to a site, I find the toilet blocks hardly used… never busy…. But when we ran a site, it was like Piccadilly Circus.
My 'van does have a shower of its own, but unless you're on a fully serviced pitch (still few and far between), you have to transport the water to the 'van, and transport it away afterwards, so, except for overnight stays in laybys, it's down to the shower block for me.
 
I would suggest that if you limit the supplies to the tourers to 10A so it gives a little bit of margin on the supply you may stand a chance of it working, as a caravanner it is very rare to get a 16A hook up most are 10A and in Europe you are very often on a 6A hook up
All protection devices will carry a little bit of overload for a time before tripping so a 10A MCB will keep it within the 16A limit likewise with the statics it may be possible to use a 25A rather than the 32A
Would have to agree with UNG. It's probably the easiest way to ensure (not guarantee) that a call to the DNO to replace the main fuse would not be needed during busy peak times.
 
it's down to the shower block for me.
Some people are scared to go in a shower block, one particular online sparks was saying how it makes him re live a few nasty experiences.

Guess the floors can be slippery or something.
 

Reply to Rcd protection for caravan hook ups in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
963

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top