The never mentioned a 30mA Si RCD. I mentioned that I had a 100mA RCD on the circuit and it kept tripping - hence the 300mA RCD
Odd, as I said previous we did at one time try 100mA RCDs but the site kicked off so we had to find a 30mA unit which worked. I personally didn't like the idea of higher than 30mA or time delay RCDs so the Si was a result. Might pay to bell them back and discuss the Si ones. I THINK I have the name of the Schneider guy I dealt with, will look tomorrow. Also can your inverter supplier not help, have they come across the issue?
gerard, clicon357,
I am just wondering why the requirement for RCD's in your environments.
Can you please enlighten us a little, as I don't see the issues from where I am to be honest.
However, as I say from where I am, I don't have the insight to the environments that you do.
gerard, clicon357,
Well I work on high rise buildings with "access equipment". So external, all weathers. Lots of 3 phase cabling supplying "cradles" or "building maintenance units". Cables from fixed outlets on the roof paid off from spring loaded drums on the machines themselves that travel round the roof edge on tracks. Then we have 3-phase cabling supplying the actual cradle (basket) that goes down the side of the building. Mechanical damage to junction boxes, limit switches / cable damage is a regular occurence with leads being run over and crushed. The people using the kit although trained to use it (and I mean no disrespect here) are only window cleaners. They want to get in press a button clean some glass and go home. Often shy of reporting damage etc. Often on a price, its a case of in/out and onto the next job. Some are even paid per "drop". Add in a couple of buckets of soapy water which sloshes about in the basket and drips over everything, wet hands changing cables etc.
clicon,
If you are suffering this much damage then the equipment being used is not suitable for the application, you have a "selection & erection" issue.
However I do understand the use of RCD's, but, IMHO this is a sticking plaster on a severed limb approach.
clicon,
You would have to understand the nature of my industry. Traditionally the cradles were simple wooden frames hoisted up the side of buildings with hemp ropes. Now we have fully powered cranes with industrial plcs some of which the users have to interface with. Whilst the kit has changed the people using it haven't. Lets be honest if they were that technically adept they wouldn't spend their days wiping dirt off glass which it what it comes down to. Its not that well paid and clients won't pay for what they see as a menial job. Its sometimes an abusive environment with time pressures. Also at the top of the building it's a case of out of sight out of mind for some clients. Bottom line is that I ventured a solution to a similar problem experienced by the OP, it worked and continues to work. Can't add much more than that really.....................
Clicon,
I am not criticising you solution per se, even though I am! Sorry! ;)
IMHO I believe that I could prove that it does not meet CDM, EAWR89, & PUWER98.
IMHO your solution relies on what is now additional protection, rather than "fundamental" protection of the circuits.
Not quite the right terminology, but I am using it that way to try to illustrate a point.
This is just my experience - and I'm sure they are all not the same. I work in a factory - if someone gets a static shock there is a big fuss, they have to go home, fill in accident reports, take time off and with today's 'compo' culture, god knows what else. Hence the reason to have everything to standard
gerard,
A "static" shock will be nothing to do with the fixed wiring installation.
In a factory environment, there are really very very limited requirements in BS7671 for RCD's.
gerard,
I understand that - I am just making a point and I don't want to take any chances. If it is possible to put an RCD on the circuit - I will
Hi,
Just an update on the RCD/Inverter problem. I talked to the manufacturers of the Inverters and they said that the problem is not the leakage current, as I have already tried a 100mA RCBO, but instead the Inverters are too small for the motors ( alarm bells did start ringing - bet they though a quick sale here!). The motors in question stop/start due to the work they carry out, so they said when a motor is carrying out a task that requires it to stop/start all the time, the inverter should be the next size up. Apparently this will solve the problem of tripping RCD on Inverter circuit. Looking forward to your thoughts.......
Cheers,
They are two 1.5kW motors and they stop/start all day long - they feed pizzas into a stamper which stops the conveyor for the time it is stamping.
OK so it's a conveyor that the inverter is driving?
Is it horizontal?
What is the make up of the conveyor?
What is the mechanical link between the motor shaft and the conveyor, direct, gearbox, belt drive?
Is it horizontal?
Horizontal conveyor, about 3m long, 500mm wide, connected with gearbox to shaft. Conveyor stops/starts to allow product to be stamped/cut to size
So basically indexing the conveyor.
Reduction gearbox I am guessing?
Motor is normal squirrel cage?
Large number of stop starts per hour, I would generally size the inverter one up from the normal duty for that motor in that application.
Though there are a few other factors I would consider.
Yes. Yes and Yes. The manufacturer recommends up-sizing the inverter like you say - he said he has seen this problem before and this will solve the problem. Not exactly the cheapest solution though!!
Incorrectly sized in the first place then really.
I'm not convinced that it will stop the tripping problem though...
Be nice to see.
Yes, and this is the second time. The first time the Inverters themselves kept tripping because they couldn't handle the motors and they were up-sized. The machine builders acknowledged this and replaced them with higher rated Inverters. Trouble was/is the old Inverters were in a very confined space and this limited the size of the new ones. They should probably have been up-sized by two sizes. I'm not looking forward to telling the boss about this as I have let it go on too long and should have notified the machine suppliers earlier - I didn't know what the problem was then.
Blimey, ....the manufacturer actually admitted supplying miss-matched/under rated inverters?? I suspect this is a ''duty'' related miss match, rather than anything else!! Have you informed them that you are still having problems with their supplied machine?? I may be, being a little nieve here, but isn't the supplier responsible for supplying a machine that is ''Fit for purpose''?? Exactly, ...how old is this machine, it must be out of warranty if they are expecting the customer to be paying for an upgrade that they should be responsible for??
If you continue to have problems with the RCD side of things, i would personally remove it, and rely on your ADS protection.
The machine builder (not the inverter manufacturer) admitted fitting an under rated VFD and replaced it - but they should have gone two sizes up as the new one was still not suitable. It's over a year old - I must dig out the details and maybe I will contact the builder to see what he has to say. If i had had know earlier i would have picked up on this and nipped it at the bud.
Have you tried the Merlin Gerin SI unit like I suggested yet?
When referring to ''Manufacturer'' i am talking about the company that supplied your company with a working (or maybe not ...lol) machine. Not included component parts manufacturers....
I put this whole question to a friend who has a lot of experience with industrial drives in fact he pointed me to the Si way back, his emailed comments are below. Wasn't sure at first what he meant by a Type B Breaker - was confusing it with a Type B MCB but pretty sure now he means a Type B (time delay) RCD.
"Next size up drive may help if,
1. The drive is getting hot, back plain running over 50dec. (bigger drive more cooling)
2. Doing fast stops without brake resistor will overload dc voltage buss.
But installing a bigger drive will not stop RCD tripping.
To improve RCD tripping you can install a Schneider Type Si or Type B Breaker."
Quite clicon,
Thing is if the d.c bus is going over voltage then we don't know how the drive is dissipating this.
It may have a bleeder system that leaks to earth by design.
This could be what is tripping the rcd.
I am not familiar with the internals of the drive that is being used.
I do know that some of the drives made by the company I worked for would bleed d.c. bus over voltage to earth via a bleeder resistor.
Depending upon the configuration of the drive this could be "seen" by the rcd as earth leakage i.e. imbalance.
If the drive was regenerative (as we called it) any surplus braking energy was converted back to a.c. and fed back into the mains.
We don't as yet know "why" the rcd is tripping on a "scientific" level.
That is what level the leakage is, at what point in the duty cycle it occurs, where the leakage is being generated from etc.
If it is the d.c. bus going over voltage and bleeding off to earth, by design and the RCD is "seeing" this as leakage and tripping, we don't know at what part of the cycle this is.
It could be at the start, it could be that the accel ramp is too steep, and that the conveyor is momentarily over speeding, and then being slowed by the drive, at which point the d.c. bus is going over voltage due to the braking energy.
Please remember some of these drives have very fast reaction times measured in fractions of a ms.
Ours had a base switching frequency of 8kHz.
I am going ordering a Merlin SI tomorrow. Meant to do itlast week but replacing a DOL 2 speed motor with an ordinary motor + Inverter on a troublesome machniw these days and am up the walls. Will have it soon
Be careful with the SI unit as the connections go from left to right, N/L1/L2/L3. I bloke I knew (alright it was me) once replaced one in a rush in semi-darkness one evening where the original, ordinary one went L1/L2/L3/N. Things went bang, smoke ensued........
Also if you wire the SI type with no neutral available then the test button doesn't work. You have to strap on a large resistor between neutral and one of the phases - I will dig out the Merlin sheet on it or post up a picture of one of mine in-situ.
I have the same problem today i have two inverters both 3 phase in and 3 phase out they knock off a 300ma rcd as soon as they start so i isolated them from all sources of earthing invluding parallel paths and they work fine but there is a fault voltage between the disconnected earths on the inverters of 14v and the earthing system . I am thinking of making this an earth free zone in a plastic enclosure. Do I need a safe isolating transformer
Were they working OK and this is a new thing? What make are the inverters? This 14V, on both? Are you sure they're not just showing natural leakage to earth? Is it a constant or just on start up?
I cant remember the make of the inverters but the voltage is constant when running. when the earths from both inverters are linked and measured between there and the main earth the voltage is 23 v. i am thinking i will set up a earth free equipotential zone inside a plastic adaptable box with all metal work inside at the same potential the cores of the sy cables are still connected to earth as normal but do i need to isolate the supply to the plastic enclosure containing the two isolated from earth inverters by means of a transformer there is no neutral entering the enclosure only the three phases . I am i suppose making an IT system or is this a double insulated system or is this a definately not. I have been reading the regs about this but im unsure any help on this matter would be apprieciated :confused:
These inverters are on a new dairy farm running the vacuum pumps its a TT system they are supplied downstream of a 300ma rcd therefore seperating these completeley from a grounded earth seems like the answer to the problem. It acually refers to this in the instruction book the make of these inverters is emerson.Im really looking for advice if i need a safe isolating transformer to supply the box. sensible replys please
the earth electrode is 34 ohms and the zs readings are much lower .......parallel paths and structural steel 16 ohms
Check which types of RCD are you using, as inverters can have a pulsating and static dc currents in the supply that can upset some RCDs. Ask the manufacture of the inverter for suggestions. Measure the current in the earth if it is excessive you may need to run the inverters off transformers. NB the star point of the secondary will need connecting to the earth terminal of the inverter, this is so the radio intereference filters can work.
RCD protection for portable equipment with Inverters
Electrician Talk | All Countries
gerard,
netblindpaul,