G
gerard
The never mentioned a 30mA Si RCD. I mentioned that I had a 100mA RCD on the circuit and it kept tripping - hence the 300mA RCD
The never mentioned a 30mA Si RCD. I mentioned that I had a 100mA RCD on the circuit and it kept tripping - hence the 300mA RCD
gerard, clicon357,
I am just wondering why the requirement for RCD's in your environments.
Can you please enlighten us a little, as I don't see the issues from where I am to be honest.
However, as I say from where I am, I don't have the insight to the environments that you do.
clicon,
If you are suffering this much damage then the equipment being used is not suitable for the application, you have a "selection & erection" issue.
However I do understand the use of RCD's, but, IMHO this is a sticking plaster on a severed limb approach.
gerard,
A "static" shock will be nothing to do with the fixed wiring installation.
In a factory environment, there are really very very limited requirements in BS7671 for RCD's.
OK so it's a conveyor that the inverter is driving?
Is it horizontal?
What is the make up of the conveyor?
What is the mechanical link between the motor shaft and the conveyor, direct, gearbox, belt drive?
Just use an inverter rated RCD
Yes. Yes and Yes. The manufacturer recommends up-sizing the inverter like you say - he said he has seen this problem before and this will solve the problem. Not exactly the cheapest solution though!!
Yes. Yes and Yes. The manufacturer recommends up-sizing the inverter like you say - he said he has seen this problem before and this will solve the problem. Not exactly the cheapest solution though!!
The machine builder (not the inverter manufacturer) admitted fitting an under rated VFD and replaced it - but they should have gone two sizes up as the new one was still not suitable. It's over a year old - I must dig out the details and maybe I will contact the builder to see what he has to say. If i had had know earlier i would have picked up on this and nipped it at the bud.
The machine builder (not the inverter manufacturer) admitted fitting an under rated VFD and replaced it - but they should have gone two sizes up as the new one was still not suitable. It's over a year old - I must dig out the details and maybe I will contact the builder to see what he has to say. If i had had know earlier i would have picked up on this and nipped it at the bud.
I am going ordering a Merlin SI tomorrow. Meant to do itlast week but replacing a DOL 2 speed motor with an ordinary motor + Inverter on a troublesome machniw these days and am up the walls. Will have it soon
I have the same problem today i have two inverters both 3 phase in and 3 phase out they knock off a 300ma rcd as soon as they start so i isolated them from all sources of earthing invluding parallel paths and they work fine but there is a fault voltage between the disconnected earths on the inverters of 14v and the earthing system . I am thinking of making this an earth free zone in a plastic enclosure. Do I need a safe isolating transformer
the earth electrode is 34 ohms and the zs readings are much lower .......parallel paths and structural steel 16 ohms