RCD protection for portable equipment with Inverters

the earth electrode is 34 ohms and the zs readings are much lower .......parallel paths and structural steel 16 ohms
 
Check which types of RCD are you using, as inverters can have a pulsating and static dc currents in the supply that can upset some RCDs. Ask the manufacture of the inverter for suggestions. Measure the current in the earth if it is excessive you may need to run the inverters off transformers. NB the star point of the secondary will need connecting to the earth terminal of the inverter, this is so the radio intereference filters can work.
 