T

tawraste

hi all,
if the main consumer unit is protected with a RCCB 80A 30mA, and the circuit has only a MCB, can i consider the sockets on the installation to be RCD protected as required by the new regs?
cheers !
 
Yes its protected, however i think you need to consider that the new regs also require that you split the ccts so that if the RCD/RCCB is tripped then not all the ccts are effected, hence the new twin RCD split boards.

My advise is if money is not an issue, either change the board to comply, or change the RCCB to a normal main switch and use RCBO's on all ccts (I prefer RCBO's if i can get them in), this does cost a lot tho.

Money and time is usually an issue ( if your only doing very little work) so I think you could just leave things as they are as long as your not adding or changing loads or stuff.

if your just doing a periodic then mark it up as a No 4, and still call it satisfactory.

Hope my rambling helps!:D
 

Reply to rcd protection for sockets in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
501
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
974
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K
You cant just "avoid" the use of RCD's for nuisance tripping... it will depend on how the cable is routed. (ie buried less than 50mm) What has...
Replies
7
Views
476

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top