so ive found out that you can test at 55v and the rcd should be on the secondary side and the rcd really should be designed for 110 use, i got there in the end and all the doubters abviously didnt know this....thanks for the pro active comments, all i need to find out now is exactly how you test it
 
you can buy megger rcd testers that let you test 110v cte, and it enables longer lengths of cable curing efli measurements......not sure how effective they are as additional protection......or how you would test the 110v rcd....i suppose using the prongs on the l e and n at end of female plugs........i can understand protecting the armoured with an rcd as the breaker is 50a in my case, but i cant get an rcbo that size.....only saying this as its an electrical forum and if i said this to my mrs she would leave me....---
 
Dave,
You were saying the supply needed RCD protection, you are now discussing RCDs on the load side two very different things!! If you want RCDs on the load side you do need ones that will work with a 110V supply voltage, ABB and others offer them, give ABB a call.
 
cheers mate, to be honest i was asked to rcd protect the site transformers, i ordered 50a rcbos to replace the 50a mcbs at the supply, they got back to me and said they didnt make them, so my mate called me and said put them in the tx, this confused me a bit and made me look deeper into it, ie now, i think they maybe would want the armoured rcd protected i would think as site transformers get moved and abused and a live cable could come out, in which case maybe i would have to mount a board adjacent to the main board and run the cables into this as i have 7 10 kva site transformerso install , unless anyone has better ideas.....how do i test the rcd on the load side if i install it
 
thanks, i was really after knowing the exact details, i e, L on L1 N on L2 and E on e.....at socket and then press test, as ive only ever plugged in the plug to the socket and pressed test.
 
Then with the greatest of respects what are you doing working on 400v and 110V systems? I have given you a link to a page that has at least 1 RCD tester that will happily do the tests that you require and you could not spot it. Are you aware of how badly things can go wrong when you short out a 400V supply? Do a youtube search for Arc Flash? What time curve are you selecting for the supply MCBs?
 
ha yeah, dont know.....didnt cover testing rcds on cte systems.....you have to start somewhere hey.....i put a 50a mcb into 1L3 in the board i worked to s spec, why do i need time curve.....its an armoured in the board to the tx...

- - - Updated - - -

its a single phase tx by the way
 

Reply to Rcd Protection For Supply To A Transformer On Construction Site? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
487
Usually if there are only C3 observations it would usually be deemed satisfactory but could be found to be unsatisfactory in unusual...
Replies
15
Views
2K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top