It would have been ok because the builder told me that the ceiling was going to be dropped about 60mm give or take, but on returning a couple weeks ago he decided to dropped it about 30 without letting me know an now its been boarded and plastered! Where does this leave me know guys, bit worried about this one.

Cheer

Paul

Walk away.
 
Im going to just have to put a 30mA RCD at the origin now regardless of reg 314 and just make a note. Really naffed off with this.
 
Im going to just have to put a 30mA RCD at the origin now regardless of reg 314 and just make a note. Really naffed off with this.
To reiterate:
The use of an 30mA RCD is not an acceptable method of providing additional protection for cables above ceilings or under floors.
Unless you also provide an acceptable method, you will fail to comply with both 314.1 and 522.6.100.
 
That 522.6.100 reg is absolutely stupid. When they brought in this 30mA protection for cables not buried at a depth of more than 50mm they should have got rid of that one. How is that even right!? What would happen if the house blew over on its side and ceiling now became a wall? An RCD is probably the best method.
 
To reiterate: Walk away (laugh and shake your head at the same time for maximum effect)

Mate, if you are really tied to this job then stand your ground and get them to remove the ceiling. They have shown you no professional courtesy.
 
So
If for example you was to install a lighting circuit for 1 light under stairs
from ccu it was in trunking
then entered the palsterboard underneath the staircase and back out on opposite wall back in trunking to the switch then onto say a batten lampholder
would this then not reqiure additional protection by means of RCD
or at the point were it entered the ceiling and came out the other side should have mechanical protection provided BY
either
metal conduit or use of SWA cable

Or jsut install
a RCD to protect the only light
or in trunking on the surface
On my mother in laws job last year for elecsa assessment
i went to point of making sure all me holes were within 0.25 and 0.4 the span of the joist 50mm from top or bottom
holes drilled 3 diameters apart
and the plumber comes along and bangs either large notches out everywhere or runs his pipes on top of your cables trapping some with heating pipes GAS pipes
and springy plastic piping looking like a large white wriggling worms all over the shop
 
The rcd is for the walls not ceilings so cable in wall less than 50mm requires rcd
cable in ceiling lying on ceiling doesn't require rcd
as you knew already
 

Reply to the thread, titled "RCD Protection on 16mm Submain??" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top