Dean31

Hi Guys,

Need some advise on RCD protection, I have just tested 112 rooms in a Travelodge in Wales and there is no RCD protection on the bathroom lights, the ceiling is over 2.25m and the light fitting is a L.E.D class 2.

Looking in the regs in section 701 & 415 and from posts I have read on here they need RCD protection but I just wanted to get a few more opinions as the hotel is only 5 years old and surely this wouldn't have been missed when designed.

Many thanks
 
If you'd have said domestic, to be honest, i'd of said forget the RCD, 2.25m high ceiling, Class 2 IP44 light fittings, what's the point!!

But it's relating to a hotel, which puts a whole new dimension on the word Safety in my book!! As daft as it may seem, you'll need to give these bathroom lights additional RCD protection, if only to cover your arse!!!
 
I am not sure, the bathrooms are completely tiled so unable to remove units to see, they are just shower cubicles and no bath. They only thing I can see from the riser cupboard on the corridors which on some of the rooms are directly behind the bathroom are earthed bolts coming through the wall.
 
I am not sure, the bathrooms are completely tiled so unable to remove units to see, they are just shower cubicles and no bath. They only thing I can see from the riser cupboard on the corridors which on some of the rooms are directly behind the bathroom are earthed bolts coming through the wall.

Any chance of a photo or two of this earthing bolt you're talking about, ....i'm intrigued?? By the way, if you haven't dropped the light fittings , how do you know for sure they are class 2 fittings??
 
Hi Guys,

Need some advise on RCD protection, I have just tested 112 rooms in a Travelodge in Wales and there is no RCD protection on the bathroom lights, the ceiling is over 2.25m and the light fitting is a L.E.D class 2.

Looking in the regs in section 701 & 415 and from posts I have read on here they need RCD protection but I just wanted to get a few more opinions as the hotel is only 5 years old and surely this wouldn't have been missed when designed.

Many thanks

This could be 2008 borderline -if the '5 years old' is estimated
The lights are definitely mains voltage (not elv), yes?
No certification from new install?
 
Last edited by a moderator:

Reply to RCD protection on bathroom lighting. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

  • Question
ok cheers for the help lads
Replies
7
Views
706
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
950

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top