putting a light and socket in loft ...light from existing lighting circuit break into ring for socket...wylex board no rcd protection ...all bonding in place do i need rcd protection for socket as all cables to be surface mounted
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss rcd protection in the UK Electrical Forum area at ElectriciansForums.net
At the moment there is no requirement to work to Amendment 3, though of course it is permitted to work to amendment 3.
From 1st July, in a dwelling, the only method available to permit the omission of 30mA RCD protection for sockets is for a specifically labelled socket for a specific piece of equipment.
In non dwellings in certain circumstances it may be possible to undertake a risk assessment that identifies that 30mA RCD protection is not required for a socket or sockets and if this is documented with the installation certificate then the 30mA RCD protection may be omitted.
i knew about the change etc but by the time i looked into specidics i couldnt change it because off lockout.I think you're contradicting yourself.