EICR
tnc-s system ....lighting circuit ......cables buried less than 50mm ....not rcd protected....what code should i put
(i think code 2...
but could it be c3 (not compliant with current regs)
 
C2 is potentially dangerous.
C3 is improvement recommended.

What potential danger are you seeing here that warrants a C2?

The most I would give that on its own, assuming no other problems having an impact on it, is C3
 
Thinking about metal fittings

irrelevant. metal fittings without a cpc would be a code C2 , but if the installation was pre 2008, the 522 6.101 did not apply , so the most you can give is a C3 for lack of RCD.
 
I think maybe it is time to to start applying codes to some of the people Carrying out Eicr's.
With the Op getting a C1
 
Code zero even!
If it wasn't so sad Damian it would be funny just how many people can't seem to code an installation correctly.
 
There's one round my way, calls himself Bradbury Electrical. He's fresh out of college, can't be older than about 20, and drives a liveried up van with 'testing and inspection specialist' written all over it. Amongst other blunders, this kid C1s 6mm bonding conductors on 60A TN-S systems. I've yet to bump into this clown in the wholesalers but I look forward to the day I do!
 

Reply to rcd protection in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
813
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K
  • Question
This charger doesn't support rear entry from the looks, only bottom entry, hence that. Unless they make a white sheathed SWA, I would still need...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top