I have a 40amp RCD downstream of a 50a MCB (10mm csa cable) should the MCB be lowered to protect the RCD from overload?
If so why does this not apply to RCD devices in Split Load boards
 
It depends on what is connected, if it is a shower for instance that is rated at 40A then no, there is no possibility of overload.
 
It's a sub DB with potentially 54a Load over 3 circuits (not accounting for diversity)
Main concern although unlikely is the potential to exceed the rating of the RCD before the MCB operates.
However this would seem a more likely thing to happen in the main CCU (Split Load dual RCD board) with a potential to exceed 150amps on that RCD alone. I understand the likely hood of this is remote but still am intrigued as to why both RCDs in the main CCU are not rated at 100a. Just seems a little strange.
 

Reply to RCD rating in Sub board less than suppy protection in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
259
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
744
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
738

Similar threads

  • Question
This charger doesn't support rear entry from the looks, only bottom entry, hence that. Unless they make a white sheathed SWA, I would still need...
Replies
8
Views
1K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
945

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top