Evening all, after a bit of advise or reference to look towards.

We protect our installations with RCD/RCBOs to protect against earth faults and stop people getting zapped. However with smart homes on the rise, and most houses now having LED lighting, plus USB sockets. The RCD/RCBOs we generally fit will only protect against AC sine wave. Why are we not installing ones that protect against DC? And why if it is an issue hasn't it been pushed in the 18th edition?

For the benefit of the ones who want to massage their ego and pick faults in my question, lets assume I'm a week 1 day 1 apprentice and I got my ECS card out of the coco pops box

Cheers

Mike
 
Designers should utilise their knowledge of the regulations and their general understanding of electrical principals to select equipment suitable for the intended use.

The regulations aren’t a step by step instruction manual for every job or situation you’ll come across, that’s why they don’t tell you what type of RCD or RCBO to fit. The designer is expected to make that decision based on the characteristics of the installation or circuit they’ve been asked to design.
 
Designers should utilise their knowledge of the regulations and their general understanding of electrical principals to select equipment suitable for the intended use.

The regulations aren’t a step by step instruction manual for every job or situation you’ll come across, that’s why they don’t tell you what type of RCD or RCBO to fit. The designer is expected to make that decision based on the characteristics of the installation or circuit they’ve been asked to design.
I agree, however Domestically how many RCD etc have you come across that protect against DC? Would you not of thought it would get a mention, it is mentioned for Car charging points
 
How common was LED lighting when RCD’s were mandated for socket outlets and split load boards became ubiquitous? The regulation writers can’t predict the future, though they do try.

I agree with the point you’re making, and there’s a good chance a future edition or amendment will incorporate it, but ultimately it still comes back to the designer to select suitable equipment.
 
The 18th edition does make reference to selecting the correct type of RCD/RCBO quite extensively compared to previous additions.
I don’t have any previous editions to compare it to, but yes 531.3.3 is all about the types of RCD and even states “the appropriate RCD shall be selected from the following:”

The IET did a whole article on it which answers your questions better than I ever could;

https://electrical.------.org/wiring-matters/years/2019/77-september-2019/which-rcd-type/

I give in, the forum keeps censoring the iet (all small letters, no space) out of that link where the dashes between electrical. and .org are...
 
Last edited:
How common was LED lighting when RCD’s were mandated for socket outlets and split load boards became ubiquitous? The regulation writers can’t predict the future, though they do try.

I agree with the point you’re making, and there’s a good chance a future edition or amendment will incorporate it, but ultimately it still comes back to the designer to select suitable equipment.
Yes I agree that it is down to the designer, it is a point I have been over looking myself. I'm glad to a degree that there isn't a technical reason why that I had missed, but I am surprised more people are not asking the same question. Cheers for your time
 
Yes I agree that it is down to the designer, it is a point I have been over looking myself. I'm glad to a degree that there isn't a technical reason why that I had missed, but I am surprised more people are not asking the same question. Cheers for your time

It’s a good question and I don’t think enough people really think about it given that pretty much every pre-populated board you can buy has type AC’s in it. That’s started to change over the last year, but I think it still holds true for most of the stock in wholesalers at the moment.

For exactly the reasons you stated in your first post I always look to fit type A RCBO’s or RCD’s now.
 
I don’t have any previous editions to compare it to, but yes 531.3.3 is all about the types of RCD and even states “the appropriate RCD shall be selected from the following:”

The IET did a whole article on it which answers your questions better than I ever could;

https://electrical.------.org/wiring-matters/years/2019/77-september-2019/which-rcd-type/

I give in, the forum keeps censoring the iet (all small letters, no space) out of that link where the dashes between electrical. and .org are...
Just looked up 531.3.3 and I have it highlighted, obviously something covered on 18th which I have brushed over, not paying it a second thought until now. Lessons learned. Cheers for the link as well
 
For the benefit of the ones who want to massage their ego and pick faults in my question, lets assume I'm a week 1 day 1 apprentice and I got my ECS card out of the coco pops box
You do know how to take the fun out of massaging my ego. In point of fact most manufacturers are not making type AC RCD any more you can only get Type A. However there is a lot of redundant stock that wholesalers are wanting to get rid of and they seem to make it difficult to get hold of Type A RCD feigning ignorance of such devices. It should now be offered as standard. BEAMA do a very good doc on RCD types/technology as well as (of all people) Dopke. There is another thread recently started asking about design of circuits when these consideration are in play. @Lucien Nunes said he was doing some testing on the very same item and would come back to us with results when he finished earth leakage testing on electronic stuff should be interesting to see his findings. Although I stated a notional (safe?) assumption of 3ma per computer, he suggested much less than that. I think I would go with his version over mine as he is undoubtedly more technically advanced than myself.
 
Last edited:
You do know how to take the fun out of massaging my ego. In point of fact most manufacturers are not making type AC RCD any more you can only get Type A. However there is a lot of redundant stock that wholesalers are wanting to get rid of and they seem to make it difficult to get hold of Type A RCD feigning ignorance of such devices. It should now be offered as standard. BEAMA do a very good doc on RCD types/technology as well as (of all people) Dopke. There is another thread recently started asking about design of circuits when these consideration are in play. @Lucien Nunes said he was doing some testing on the very same item and would come back to us with results when he finished earth leakage testing on electronic stuff should be interesting to see his findings. Although I stated a notional (safe?) assumption of 3ma per computer, he suggested much less than that. I think I would go with his version over mine as he is undoubtedly more technically advanced than myself.
Haha, I think I did fairly well in the comments (so far) considering there is a reg about it. But every day is a school day, I normally fit B type RCBO's mainly because that's always been the norm on site. But I don't want to fall foul of the "I know what I like and I like what I know" attitude. I would also be interested to see his findings.
 
RCBOs with type B for RCD are quite rare, most are type B for the magnetic over-current trip.

Yes, that is a whole tin of WTF over the choice of identification!

I expect that soon you will only see type A RCD/RCBO being sold as the UK moves towards the same sort of guidance as the EU where type AC is pretty much banned due to the high likelihood of a DC component in fault currents.

However, it is not as simple as Type AC not tripping on a pulsed current DC/AC waveform, sometime they will trip but not always as specified (maybe higher current or slower, etc). The point is type AC is not warranted to work under those conditions, and can be blinded by high DC components saturating the sense transformer, so you should not be using them where equipment is rectifying the mains for its application, and these days it is a lot of stuff.

However, we also have the rather stupid situation of electrical wiring having to fit RCD capabilities suitable for general purpose sockets and no guarantee of what sort of a load can be attached to them!
 

Reply to RCD/RCBOs DC Fault in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
356
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
909
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Protection from what? What kind of problem with the inverter is going to be helped by having an RCD on the circuit?
Replies
5
Views
2K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top