Hi guys,
Just a quick query here. I have just gone into a property and done a EICR. Its a rewireable fuseboard with no rcd protection on any circuits. The main house ring circuit has an occurence with a spur off a spur. Easy to rectify i know but as i am going to to re-feeding the sockets, is there any requirement for me to protect the circuit with an RCD?

Many thanks in anticipation,
Dave
 
Hi guys,
Just a quick query here. I have just gone into a property and done a EICR. Its a rewireable fuseboard with no rcd protection on any circuits. The main house ring circuit has an occurence with a spur off a spur. Easy to rectify i know but as i am going to to re-feeding the sockets, is there any requirement for me to protect the circuit with an RCD?

Many thanks in anticipation,
Dave
Just from what you have said, C2 for no RCD for socket outlets, C2 for multiple spurs - overload risk, C3 for No RCD for cables concealed <50mm in walls. Quote for new CU and rectify ring spurs. Nice little remedial for you.
 
Just from what you have said, C2 for no RCD for socket outlets, C2 for multiple spurs - overload risk, C3 for No RCD for cables concealed <50mm in walls. Quote for new CU and rectify ring spurs. Nice little remedial for you.

why is a new CU required?

he is merely asking if any work he carries out needs RCD/RCBO protection.

Oh and sockets without RCD/RCBO protection is a C3, if it complied when installed, unless they can be used outdoors.
 
why is a new CU required?

he is merely asking if any work he carries out needs RCD/RCBO protection.

Oh and sockets without RCD/RCBO protection is a C3, if it complied when installed, unless they can be used outdoors.

Just from what you have said, C2 for no RCD for socket outlets, C2 for multiple spurs - overload risk, C3 for No RCD for cables concealed <50mm in walls. Quote for new CU and rectify ring spurs. Nice little remedial for you.

Rephrase that to “nice little earner for you.”
 
It seems to be meggermans standard response to every post about doing a job in a house without RCD protection.

Ok, in complete contrast to your make do and mend philosophy, which then will get done by someone else later and they can pay again. Also as Inspector it is my discretion what I code non-compliances. Maybe you worth noting it would be reasonable to expect that any downstairs socket outlet could be used to supply equipment outside.
 

Reply to RCD required? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
936

Similar threads

  • Question
I seem to find two types of installation in older houses in which electric showers have been added: those with shower fed from an MCB without RCD...
Replies
9
Views
839
nicebutdim
N
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top