Hi guys,
Just a quick query here. I have just gone into a property and done a EICR. Its a rewireable fuseboard with no rcd protection on any circuits. The main house ring circuit has an occurence with a spur off a spur. Easy to rectify i know but as i am going to to re-feeding the sockets, is there any requirement for me to protect the circuit with an RCD?

Many thanks in anticipation,
Dave
 
Ok, in complete contrast to your make do and mend philosophy, which then will get done by someone else later and they can pay again. Also as Inspector it is my discretion what I code non-compliances. Maybe you worth noting it would be reasonable to expect that any downstairs socket outlet could be used to supply equipment outside.

Make do and mend yes, they are asking to repair a small part of the installation not change i all completely, besides installing a new DB could lead to a whole load of problems which would cost the customer even more money that they didn't need to spend.

Yes the coding is down the inspector, as I said no question was asked about coding.

Again I pointed out if the sockets could be used outdoors, please read the whole reply before replying as it just makes you look ignorant and choosing what you want too read.
 
Make do and mend yes, they are asking to repair a small part of the installation not change i all completely, besides installing a new DB could lead to a whole load of problems which would cost the customer even more money that they didn't need to spend.

Yes the coding is down the inspector, as I said no question was asked about coding.

Again I pointed out if the sockets could be used outdoors, please read the whole reply before replying as it just makes you look ignorant and choosing what you want too read.[/QUOTE

I did read you post. Oh and sockets without RCD/RCBO protection is a C3, if it complied when installed, unless they can be used outdoors. . I am saying they can all be used outdoors.
Also, the guy has just carried out an EICR, this is the best time to now carry out DB replacement as he has inspected and tested installation so knows what faults are present. Why would that lead to problems?
 
I would say only sockets in a room with a external door on it would be used outdoors. I have a socket on my first floor landing no external access unless you walk past several other sockets first, I also have several sockets in my kitchen which has a back door and one in my hall ways which has the front door leading outside. Now would you say the landing socket or any other socket upstairs needs RCD/RCBOprotection, if it was installed when it wasn't needed?
 
This is not a pop megger but have you somehow ordered an excessive amount of DB's by mistake because I have to agree with others that this seems to be your standard reply to every thread relating to domestic rcd threads.
I know we are all in business to make money but do you ever try to rectify a job in a cheaper way or just rip it out and start again
 
I would say only sockets in a room with a external door on it would be used outdoors. I have a socket on my first floor landing no external access unless you walk past several other sockets first, I also have several sockets in my kitchen which has a back door and one in my hall ways which has the front door leading outside. Now would you say the landing socket or any other socket upstairs needs RCD/RCBOprotection, if it was installed when it wasn't needed?

No, If separate circuits up and down, personally, I would only C2 downstairs sockets in a house and would C3 upstairs (5.12) as I would not reasonably expect upstairs sockets to supply equipment outside.
 
This is not a pop megger but have you somehow ordered an excessive amount of DB's by mistake because I have to agree with others that this seems to be your standard reply to every thread relating to domestic rcd threads.
I know we are all in business to make money but do you ever try to rectify a job in a cheaper way or just rip it out and start again
Honestly, I do not have a pile of DB's in my garage I cannot shift :). I like to leave a job as safe as possible, and if I can make it safer I do. I do give them the options, (add on RCD etc) but when I explain the advantages they nearly always go for it. I am only ÂŁ250 for new 5+5 DB installed, cert and registered. 90% of my work is repeat now, so I must be doing something right :).
 
I recently provided a RCD socket as part of an EICR remedial list. It was the nearest to the back door into the garden and was labelled and explained it was the dedicated socket for outdoor appliance use. This set the customer back ÂŁ25. Should I have informed my 94 year old customer that a ÂŁ250 CU change was the only way forward ?

To the OP... yes you need to RCD protect any socket circuit you go jiggering about with. You and your customer can discuss the best method to comply with this that is suitable for both parties.
 
Meggerman that is bloody cheap you want to be at 350.00 I would think
 
Hi guys,
Thanks for the feedback. A lot of it is down to personal opinion to be used in conjunction with the regulations. The EICR showed the installation had a clean bill of health. The zs readings were good and the I.R readings were also very good. There would be no issue at all with installing a new fuseboard.There are no spare ways on the fuseboard and the client has indicated that he will be having work doing in the future so i shall advise him that it may be prudent to get an up-to-date system now as he will definetely require one in the not too distant future.
 

Reply to RCD required? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
312
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
941

Similar threads

  • Question
I seem to find two types of installation in older houses in which electric showers have been added: those with shower fed from an MCB without RCD...
Replies
9
Views
840
nicebutdim
N
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top