I'm having a complete mind blank on what the mA requirement is for an RCD on domestic household with TT earthing, Ra = 57ohms. I'm not talking about final circuits.

I'm planning on splitting the meter tails into a henly, then into a switched fuse, then 50m SWA to consumer unit in garage which will contain a 30mA RCD or RCBO's.

I simply cannot remember or find in the regs if I need RCD protection for the buried SWA. If it was a TN then It wouldn't need it as it has mechanical protection, but it's TT.

I'm sure a 100mA S type would be OK in the switch fuse as replacement for main switch, but I just want to know where in regs it says this will comply, or even necessary?
 
So if you want to fit an EVSE on a TT supply with upfront S type you effectively can’t?
That's the conclusion I'm arriving at, if the charger requires Type B RCBO, and why I'd directed the question to Risteard. I figure he might have considered this possibility.

Edit: Just spotted @Ian1981 post, which seems to confirm this thought.

There doesn't yet appear to be a great selection of available 2 pole time delayed 100mA Type S RCCBs, with Type A characterisitcs and I'm surprised that Wylex haven't yet introduced a version of the widely used WRMT100/2. Currently the best priced and most widely available options appear to be those from CP Fusebox and Lewden.
 
Last edited by a moderator:
Not that I have seen. Doepke have a good range of type B (at a price!) but none are delay ones to mk knowledge.

As best I can ascertain, they manufacture a couple of industrial Type B time delayed RCCBs, but nothing suitable for a typical domestic installation.

DFS4 B and DFL8 B
 
But how much?

I would consider anything more than a few mA to be a fault, as one would expect the system (even at 48V or whatever considered "safe") to have insulation resistance of hundreds of kohm to earth.

If the EV charger is OK for a 30mA type B RCD than it would have to be below 15mA normally, or it is in the trip region. And as above, I can't see that sort of level saturating any type A RCD, and not a 100mA (or above) type AC.

If you had it off a 30mA AC RCD/RCBO I would be a bit more concerned

But for playing with some type-AC RCD FCU recently they would trip on the type A waveform OK, just too low current in one direction, and a little slow in the other direction.

So for sure if you could have significant DC then you need type B, but upstream of that I can't see it causing difficulties for any that are going to be selective anyway (so 100mA or above TT incomers).
From my understanding A type are up to 6mA and F&B types are up to 10mA. Without knowing the manufacturers information I couldn't comment on how much leakage they have but some do stipulate B type RCDs so it must be a fairly high current they generate during normal use.
 
So if you want to fit an EVSE on a TT supply with upfront S type you effectively can’t?
You can. I did two recently for a well-known major courier company.

One was single phase and I replaced the Type AC S-type with a 300mA Type A S-type, along with a Type A 30mA for the EVSE - which had inbuilt 6mA DC leakage protection.

The other was three-phase so I replaced the Type AC with a four pole 300mA Type A S-type, and a four pole Type A 30mA for the EVSE (again with built-in 6mA DC leakage protection).
 
That's the conclusion I'm arriving at, if the charger requires Type B RCBO, and why I'd directed the question to Risteard. I figure he might have considered this possibility.

Edit: Just spotted @Ian1981 post, which seems to confirm this thought.

There doesn't yet appear to be a great selection of available 2 pole time delayed 100mA Type S RCCBs, with Type A characterisitcs and I'm surprised that Wylex haven't yet introduced a version of the widely used WRMT100/2. Currently the best priced and most widely available options appear to be those from CP Fusebox and Lewden.
Sorry, was working until 8:30p.m. tonight so only seeing your post now. I haven't come across an RCBO with a Type B RCD characteristic (though they may exist). Any Type B RCD I have fitted has been an RCCB.

If a Type B RCD is needed then any upstream RCD will need to be Type B also. If Type A, then any upstream will need to be at least Type A.

You shouldn't have any issue finding a double pole Type A S-type RCCB - they are widely available.
 
Sorry, was working until 8:30p.m. tonight so only seeing your post now. I haven't come across an RCBO with a Type B RCD characteristic (though they may exist). Any Type B RCD I have fitted has been an RCCB.

If a Type B RCD is needed then any upstream RCD will need to be Type B also. If Type A, then any upstream will need to be at least Type A.

You shouldn't have any issue finding a double pole Type A S-type RCCB - they are widely available.

No worries about the time and I appreciate the response - it was purely hypothetical and came to mind after Type B requirement for certain chargers was introduced in post #17.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
-
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
RCD requirements for TT?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
47
Unsolved
--

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
pc1966,
Replies
47
Views
17,501

Advert

Back
Top