A new shower circuit has been installed into a town property that is a TT earthing set up. The shower is protected by a 60amp 30 ma rcd and a 40 amp breaker. The ZS is 9.8 ohms, the Ze is 9.7 oms. Should this circuit be protected by a further 100ma rcd before the 30ma rcd or is the 30ma rcd adequate.
regards
the 30mA RCD is adequate to protect the shower circuit. however, a 100mA S type up front is a good idea on a TT system to achieve disconnection times for the installation as a whole.
(Warning: me newbie). The upfront RCD will also protect the cable between it and the shower DB with the RCD+MCB in it (I assume that's what you're talking about) which may be a requirement e.g. if the shower cable is buried in a wall.
the 10mm cable is in trunking at ceiling height from the db near the front door to the 1st floor bathroom. no other circuits are on the db.
Where's the RCD and breaker for the shower located?
- - - Updated - - -
Or do you mean that's what's by the front door?
Hi guys do you have to allow for surge protection now on over head mains now?
Just a thought:)
The 30mA RCD is more than adequate in providing the required disconnection time for the shower circuit. It also provides additional protection as per the requirements of section 7 in the BGB regarding special locations therefore you do not need to install an upfront type S but in many cases it would be prudent to do so.
Cables buried in walls less than 50mm require additional protection by means of a 30mA RCD, therefore a 100mA RCD would not be sufficient to protect it.
QUOTE]
Not on a TT earthing system it doesn't, it's the ONLY means of earth fault protection!! And why having a 100mA S type RCD up-front, is a prudent additional/back up protection. This mainly due, because RCD's as a whole, are not particularly known for their reliability as yet!!
I don't understand what point you disagree with Eng? A 30mA RCD does provide additional protection regardless of what the nature of the supply is, even if it is the sole means of providing earth fault protection also.
ADS is the primary earth fault protection on TN earthing systems, with 30mA RCD protection providing the ''Additional'' protection. On a TT system however, the ADS is basically null and void and in most cases, unable to provide any form of earth fault protection!! The 30mA RCD is then providing the sole means of earth fault protection. Which is all fine and dandy while the RCD is functioning correctly. So it can't really be classed as Additional protection can it, it could i suppose be classed as an enhanced form protection... lol!!
It can be both. It is providing both fault protection and additional protection. As I said in my first reply, the OP doesn't need to fit an upfront RCD but it would be prudent for him to do so, that way, if the 30mA fails, yes the customer may lose their additional protection but at least they still have their fault protection. If he didn't, he wouldn't be breaking any actual regulations.
I was merely satating the facts and in no way advising him. Anyway, we're arguing the same fundamental point regarding it being a good idea to fit an upfront type S lol.
How do you arrive at the conclusion that ADS doesnt apply to a TT system???.....ADS is the standard protection against electric shock on all the commonly used systems in the UK,including TT,where ADS is usually achieved by nmeans of an RCD.
By ADS perhaps i should of stated conventional means of earthing!! RCD protection is classed as ''additional'' protection on TN systems. It sure ain't additional protection on a UK TT earthing system is it?? It's RCD or it's nothing!! ...lol!!
I totally understand what you're getting at but technically speaking, you're wrong.
An RCD of any size on a TT provides fault protection, a 30mA rating will provide additional protection.