Doing standard tests prior to some minor works on a socket circuit (Zs, IR etc), pressed the test button on the RCD, tripped fine, got ready to measure trip times but the RCD would not reset. Tiny bit of resistance as you first start lifting the lever, then goes completely floppy, i.e. you can lift the lever but it's not engaging with anything, and doesn't hold. Tried a few times but would not reset.

Disconnect the N out of the RCD, (all downstream circuits already turned off), and this time the RCD reset. "Ah!" I thought, "Maybe some pretty serious N-E fault is preventing me resetting it!" So like a fool I pressed the test button again - it tripped - and then wouldn't reset. Tried turning off the main switch - no difference, still won't reset.

So off I go to the van, to see if I've got something that fits well enough before I can get a matched replacement by the same manufacturer. By the time I come back from the van, I can reset the RCD.

At this point, I figure it just needs a little rest before being reset. Sure enough, I managed to do all the standard RCD tests, all disconnection times were well within spec, it just needed 2-3 minutes after tripping each time before it could be reset.

It is a Contactum B6303/2: BS EN 61008, 2-pole, 63A, 30mA, type AC.

Anyone experienced anything similar?
 
Yes with the exact same RCD. Changed a shower pull switch, did some basic tests and the RCD wouldn’t reset. Went to the wholesalers and picked up a newer contactum RCD. Got back, reilised the new one didn’t bloody fit and then the old one reset in my hand and tested out fine!
 
There are a pair of those RCDs not ten feet from where I'm sitting and never had any issue with resetting after pressing the test switch. Replaced one after about a year, when it became overly sensitive and progressively more difficult to reset after each trip.
 

Reply to RCD requires a little rest before resetting in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Merry Xmas to all :D
    • Friendly
    • Like
Replies
8
Views
452
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
747
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
514
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
747

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top