M

martynp

Just taken over a new client, their HQ had a PIR carried out a few weeks ago by a third party company, they have stated that 75 MCBs require changing to RCBO's because the are not under the supervision of a skilled or instructed operative as stated in BS7671. There are NO hazzardous areas in the building (they are all paper pusher).

How do you interpret the reg for this one, it seems a little over the top. I think it was their way of making work for themselves.

Comments please.
 
thats a 17th edition regulation, if the installation was designed and constructed to 16th edition, then it's a code 4 and it doesn't require updating.
 
Sounds like a money making scheme to me too.... Point your client in the direction of the ESC's periodic inspection reporting guide, and tell them to show it to the contractor and ask where no RCD in an office is anymore than a code 4...
 
The previous contractor was correct in quoting the BRB, in that socket outlets will not be under supervision,, blah blah blah... and if you were at the design stage you would have to include RCD/RCBO protection for current regs.

But as others have stated, its a 4 at best.

You can win some brownie points with the client by highlighting the most vulnerable circuits and dealing with them first..!!
 
No outside stuff at all.

Who is a "skilled" or "instructed person"

BTW they have put it down as a code 4 but implied they need to be changed.
 
Yeh code 4 m8.

still a lot of confusion amongst some testers, who think that because an installation is being tested to the 17th edition, that a 16th edition installation automatically fails
 
My own take on the skilled or instructed person definition in your example would be,is there any likelyhood that an unskilled person(ie the pen pushers) going to drill the walls ?

The probability is no,and that imported skilled or instructed persons would be doing those things

I would ask the client for a signed statement of that intention and then omit the Rcbos
Alternatively instruct him yourself and ditto
 
I would cite code 4 also. besides that, if there are no skilled or instructed persons on site, who would be testing the RCBO's every month.
 
It refers to people electricaly skilled (or so instructed) or otherwise knowledgeable about those particular surroundings.

"Both persons with some electrical knowledge and those with none may be classified as
instructed persons."

So INSTRUCTED people could be anyone, if they have received appropriate input "by skilled persons, to enable them to avoid dangers which electricity may create"

One example given during my 2391 course was a socket outlet in an office/factory, not RCD protected because it was for use with a particular piece of equipment which only operators who had been trained were allowed to use. So far so good.
On that basis alone, no RCD protection required. Even though the operators werent "electricaly" skilled, their use of it from that particular outlet was such, that only those who had received training on the equipment would be using the equipment and these people were aware of relevant health and safety procedures, ie isolation for cleaning, malfunctions, and switch off procedures. All hunky dory.

However, at the end of play each day they went home, in came the cleaners, and plugged the hoover into the same outlet..!

Now unless the cleaners had been on a (good) course covering how to use the hoover and the implications of an electrical fault... or under the supervision of such.. RCD required..!

So more than likely you wont have any "skilled or instructed" persons at those offices. With perhaps an exception of any IT technicians..
You will have mainly "ordinary" persons, as BRB calls them.

Perhaps putting all the staff on an "electrical health and safety" course.. ie an hours worth.. would then classify them as "instructed"..?!
And would probably be cheaper than 75 RCBO's.. haha
 
Last edited by a moderator:
Hey guys.

With reference to the above,

We are changing an old re wirable fuseboard in a school and are having dicussions with regards to instructed persons etc.

We are going to put al existingl outgoing sockets on an RCBO as this will bring it upto date as cleaners and any other "ordinary people" can use them. However we are not sure whether the lighting circuits (when chased in a wall less than 50mm not protected etc etc) also need to be put on RCBOS as they have a caretaker on site that can be deemed "an instructed person" ?

what are your thoughts on this?

many thanks
 
Hey guys.

With reference to the above,

We are changing an old re wirable fuseboard in a school and are having dicussions with regards to instructed persons etc.

We are going to put al existingl outgoing sockets on an RCBO as this will bring it upto date as cleaners and any other "ordinary people" can use them. However we are not sure whether the lighting circuits (when chased in a wall less than 50mm not protected etc etc) also need to be put on RCBOS as they have a caretaker on site that can be deemed "an instructed person" ?

what are your thoughts on this?

many thanks

A lot of the older schools had steel conduit chased into the walls so it might not be necessary to use RCBO's
 
I suppose technically, the caretaker is a skilled and instructed person and no members of staff or pupils should be hammering nails into the wall.

I think to make sure, have a word with tech support at your scheme provider.
 

Reply to RCD - Skilled or Instructed Person in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top