C

charlhu

I recently replaced an old electric cooker with an up-market multi-function ELO and ceramic hob that I had kept in storage for 4 years - a simple swap at the cooker switch. The Wylex domestic CU was put in 4 years ago and incorporates a WRS 80/2 30mA RCD and has never given any problem. There is never a problem switching the ELO "ON" and operating it but every now and then (but not always) when the programme selector switch is turned back to the "OFF" position the RCD trips. This can also happen if the cooker switch is turned off. The ELO and hob go through the same cooker switch via a junction box but the hob never causes an RCD trip. I don't want to have expensive call-ins on a problem that cannot be reproduced at will especially when it is unclear whether it is an electrical or an appliance problem. As I see it, if there was a leakage problem with the ELO it would always trip the RCD when switched on. I wonder if it might be a cable fault? I used the existing cables still connected to the two units to feed the junction box. Have rechecked the connections half-a-dozen times.
Grateful for any advice/suggestions!
 
Neutral isn't switching as quick as live when you turn it off, imbalance, rcd trips

I was thinking of something like that, but it still must indicate a fault condition somewhere. Ie there must still be a leakage to earth to allow the unbalanced current to flow.

My guess would be an issue with the appliance, but it could be with some of the new cables / junction box I think the OP said had been added.

And (responding to something in the first post) no, a fault with the appliance would not necessarily appear all the time because it may be related to a particular function or action, such as turning off.

Get someone in with a test meter, who can also check that the cables which were up to supplying the old electric cooker are up to powering a ceramic hob and ELO (Electric Light Orchestra??!)
 
I did think perhaps there is now something "sticky" in the controls due to storage but it only happens with a simple on/off operation - even if the oven has been left to cool down first (even overnight) so that rules out a relay or thermostat?
 
The solution would be to get an electrician in who can fully test the circuit RCD itself, and also PAT test the appliance to see if the speculations above are correct...

After that, repair whatever turns out to be faulty!
 
Thanks for your contribution. ELO = Eye Level Oven (Sorry!).
Cable from board to cooker switch is the built in wiring. I put this on to the junction box and from there fed the two units using the cables that were used in their previous location and still connected up. I wondered whether there might now be a partial internal insulation breakdown in the one cable that is causing it?
 
I wondered whether there might now be a partial internal insulation breakdown in the one cable that is causing it?

Yes, it might be that, although if it was that the tripping would probably be more random and not seeming to be related to a particular action.

My main point is... it could be any of these things, so best to get it tested rather than keep speculating!!
 
Not sure I understand what's meant by neutral not switching as quickly as live, the neutral won't normally be switched, only the live?

There is a potentially dangerous appliance that should be checked out. What's unusual in this case is the tripping happening when the oven is turned off.

Obviously if there is an imbalance the current is going somewhere, that's either to earth (via cpc) or to a device capable of charge storage (most likely a capacitor) or via a sufficiently inductive load.

Assuming the circuit supplying the appliance checks out OK. I'd then start by contacting the manufacturers technical dept and see if there are any compontents in the ELO controls that might explain the behaviour. Then IR testing the oven (once it has been warmed up, don't forget to isolate it after warming though ;)).
 
Thanks but, as stated in my post, that is the costly solution that I am trying to avoid to what may be a simple problem. Logically,the RCD is fine since, as also said in my post, there was no problem before I installed the oven in question. If I can first identify whether the problem is wiring or the appliance then in the first case I can fix it myself and in the second case probably need to call in an appliance technician but at least that is only one call-in.
 
Not sure how you can assert that the RCD is fine. Just because it didn't trip before. The RCD will trip at a certain current, nominally 30ma of leakage (or imbalance between line/neutral) ..... some will trip as low at the low 20ma's and still deemed to be working correctly.

Do you have the necessary equipment (and skills) to do an insulation resistance test on the wiring?
 
Last edited:
You are right that, being a domestic installation, it is switched on the live only. Unfortunately, this is a "Scholtes" top-range unit that I bought and used in France and the brand (now owned by the Merloni Group) is no longer distributed in the UK. Any consumer who has had experience with the technical support for any of their products (e.g. Indesit) would probably recommend the hemlock option!
I would have more confidence in a competent independant repairer who can tackle any brand but finding one is also a problem. Any dicky component is likely to be a "bought -in" item and findable. BTW, I am in London E18.
 
I wasn't suggesting that the componet would be faulty :D ... it may be a valid part of the control design, but may explain the occasional nuisance tripping.

If there is no socket on the cooker isolator switch then you could consider taking the circuit from a non rcd protected side of the CU, but I wouldn't recommend it.

Another option to consider would be a more fault tolerant RCBO (type C) for the cooker circuit. These are nomally used for circuits supply motors and other largely inductive loads. However! You need to prove the cooker is OK for use before going down that route.
 
Your theory would be correct if the RCD is inclined to trip at a level below it's 30mA rating and nothing else in the house has a low-level leakage but this oven does. That would explain the "new" problem. I don't have the kit for insulation resistance testing or testing the RCD but would modestly claim the "skill". I am a pro mechanical engineer and that requires a good working knowledge of industrial electrical installations but do not claim to be an "electrician" beyond the commonsense DIY stuff.
I now think it is unlikely to be the wiring in the light of another helpful post which pointed out that if that were it the trips would not occur only on the On/Off function.
 

Reply to RCD (sometimes) trips on switching OFF an ELO in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
Ok I’ll try this when I’m down
Replies
4
Views
398

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top