Hi, can anything else cause a RCD test button to fail, besides a faulty RCD.
Not really as I believe it is just a mechanical feature of an RCD to test the mechanics of the device that it would operate in event of a fault and not 'stuck'!
Lack of earth.
Not on any RCD I can recall. Test button connects a resistor between one pole on the input side and one of the other poles on the output side, creating a 30mA or so difference (on a 30mA RCD) between whatever current is flowing through those two poles.
No earth connection involved.
you may well be correct but I have known some rcbo's to not trip when the flylead is disconnected.
Possibly an extra test built in to ensure that the earth lead is connected, but not since the days of the old voltage operated earth leakage detectors (yes, I am that old), has there been a requirement for a current to flow in the cpc for said breaker to operate. RCDs detect a difference in the sum of the currents flowing through its poles. The sum should be zero, but if exceeds 30mA, then off it should trip.
Reply to RCD test button in the UK Electrical Forum area at ElectriciansForums.net
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...