rcd test tripping both sides | on ElectriciansForums

Discuss rcd test tripping both sides in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

E

electric8

can anybody help i did a rcd test on a circiut on a split load board and it triped out both sides of the board . I then tested a circuit on the oyher side of the board and that rcd did then not trip .I have checked for any neutrals on the wrong side but cant see anything obvious .never come across this before and wondered if anybody knows what would cause this
 
Its a new board just fitted and all new circuits in a house renovation I assume builders have fitted it and I was asked to test, all dead testing was fine 3 rings and 2 lighting all rings fine all r1 r2 fine all IR >299
 
disconnect all the circuits. then test RCDs. if they test OK trhen reconnect each circuit and test RCDs after each one. that'll trace the circuit that's causing the problem.
 
This sounds like a problem that I had a couple of years ago. I did the house rewire but it gets tested by the company spark (dont ask, he is a long story). Everything tested out great (as it should on a rewire) but when he put the cables back into the terms he did not mark them.......

He crossed over the incoming and out going legs to both RFC on both sides of the rcd's plus put a neutral in the wrong bar on one of the light circuits. What a rounded door handle.


Do a soft IR test on your L+N bars and see if something has been crossed over. Then look at each circuit one at a time (I'd start at the RFC) and identify each leg. The rest is just fault finding. good luck and give us an update with what youve found.
 
Is the db itself wired right? As in manufacturers connections?? Had one that wasn't recently.
Or is is a split load (16th)
So the two Rcd's are in series? Effectively.
Hope this helps.
 
Thanks for that suggestion sounds like I will have to get involved in other peoples work i just wondered if i was missing something simple as all looks ok in the board and all the other tests are fine all wiring looks fine
 
Yes checked all legs on rings and removed and reconnected all the circuits just to make sure that everything was in the correct neutral bar .The factory conections also look correct but they are in series
 
Yes checked all legs on rings and removed and reconnected all the circuits just to make sure that everything was in the correct neutral bar .The factory conections also look correct but they are in series

Are they both 30mA??
If one is feeding the other then it should be a S type for discrimination.
But then you wouldn't have additional protection for those circuits (if required)

Sounds like a typical builder install.......
'This board was cheaper!! I could just put a Rcd that side too'!!!!!
Lol
 
RCD's wired in series.?? i would start there.. dual rcd boards with 30ma protection usually come factory wired in parallel.!!

Sounds like a 16th edition to me, and the main sw has been changed to a Rcd!
Probably because they were cheaper and the builder wouldn't know the difference.... Lol
 

Reply to rcd test tripping both sides in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Replies
0
Views
492

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top