RCD test ... What does this mean? | on ElectriciansForums
Discuss RCD test ... What does this mean? in the UK Electrical Forum area at ElectriciansForums.net
Embra
I came across "RCD was working fine with x1 29 x 5 16 and functional test was tripped twice". What does that mean?
(I'm not an electrician.)
A little bit more information would have been nice, but I assume this was on an Electrical report, if it was, it looks like the tripping time in ms for a 1xI∆n test @ 29ms and a 5xI∆n test @ 16ms tested at 0 and 180 deg's.
Have a look here:
I think so. That and a bit of googling.
My inference is that tripping at 29ms for a type S would mean the RCD is faulty. Type S should last way longer shouldn't it? I think I saw type S are max one second, so anytrhing over 500ms is acceptable.
Reply to RCD test ... What does this mean? in the UK Electrical Forum area at ElectriciansForums.net
It can also mean lasts or continues for two years.
L
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
davesparks
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Have you notified Building Control of these works?