I came across "RCD was working fine with x1 29 x 5 16 and functional test was tripped twice". What does that mean?
(I'm not an electrician.)
(I'm not an electrician.)
Discuss RCD test ... What does this mean? in the UK Electrical Forum area at ElectriciansForums.net
On site guide section 11. Type s should trip between 130ms and 500ms.I think so. That and a bit of googling.
My inference is that tripping at 29ms for a type S would mean the RCD is faulty. Type S should last way longer shouldn't it? I think I saw type S are max one second, so anytrhing over 500ms is acceptable.