Yes I should add that I have always tested with loads unplugged.

As for the reason its not for convenience, I just think if you test at the furthest point you are taking a worst case scenario the same as you would with a PSC test or R1+R2 test.

As for the wondering round thing sometimes that is the case, Years ago before everything was labeled up properly we used to quite literally just plug the tester into a random socket and see if it tripped to fine what RCD's were feeding what circuits!
Thankfully times have changed and we now have the luxury of labelled sockets and site experience LOL
 
Was talking to spark only this week about RCD testing and he does a bit different to how I've been told to. He was saying he has been told to do test RCD the Niceic way.
His way......1. function test button.....no point testing if seized up. 2. 1 times test 0-180 3. 5 times test 0-180
4. half test..shouldn't trip ( RCD now warmed up after test 2 & 3). Is this correct?
 
I test at a socket because it's simpler to just plug in rather than faff with probes. If it fails, then it's time to get the cover off the board and test further.

If the circuit is connected properly at all fixtures and within the maximum length specified under 17th ed. then I don't see why you couldn't get reliable results at any point on the circuit.
 
You test RCD devices at it's terminals, (unless otherwise stated by the manufacturer) you're testing the device itself, not the whole damned circuit which should have been fully tested prior to any RCD device testing!! Nothing wrong with testing at a socket or at some other point on a circuit, for checking and /or fault finding. But for official recorded testing purposes, all testing should be conducted at the CU/DB....



As for testing sequence, leave that to your RCD/MFT test equipment!! As far as i know they all have a programmed sequence that you follow!! Normally the half rating tests are performed first, then the full rating tests followed by the 5 X tests
 

Reply to RCD testing - 2 chains of thought. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
706
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
502
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
736

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top