I was called in to follow up some nuisance tripping in a country cottage, which was 2 properties knocked into 1.
There are 2 CUs in the property, one at the East end of the property and one at the West end, there are still 2 earth electrodes.
Only one distributor supply now exists and this comes into the East end of the property next to CU-East.
The supply is split via some Henley blocks and one pair of tails feeds CU-East and the other goes into an enclosure
containing a 100A/100mA time delayed RCD from which the other CU-West is fed via a distribution circuit of 10mm T+E.
CU-East is a 10way protected by a 30mA RCD, there has never been any nusiance tripping on this half of the property.
CU-West is a 10way split CU protected by two 63A/30mA RCDs.
Having sussed the cause of the nuisance tripping I was in the process of running through my RCD tests to confirm compliance.
Zs at the origin and at CU-East are both good for a TT installation at 3 ohms.
The RCD test results were as expected except the last one.
In summary: 0.5I >1999 notrip / 1I @ 0degs 7.7msecs / 1I @ 180degs 18.2msecs / 5I @ 0degs 4.4msecs (last 3 all
tripped the local RCD) . . . but I5 @ 180degs 8.4msecs but tripped the 100A/100ma RCD at the supply end of the CU.
This overall result was the same for the other RCD in CU-East. All results as expected except the I5 test @ 180degs
tripping the 100A/100mA supply RCD not the local 63A/30mA RCD.
This happened repeatedly and was testing at the CU with all loads off.
I had already done R1 + R2 + Rn and insulation tests on the 10mm T+E feeding the CU-East and these were as expected.
But just to rule it out completely I re-installed one of the CU-East 63A/30mA RCDs next to the 100A/100mA time delayed RCD
via a short length (250mm) of 2.5mm T+E. I repeated the RCD test sequence and exactly the same occurred.
Can anyone suggest what might be going on here or suggest what steps to take next?
PS tester is Megger 1502/2.
I was called in to follow up some nuisance tripping in a country cottage, which was 2 properties knocked into 1.
There are 2 CUs in the property, one at the East end of the property and one at the West end, there are still 2 earth electrodes.
Only one distributor supply now exists and this comes into the East end of the property next to CU-East.
The supply is split via some Henley blocks and one pair of tails feeds CU-East and the other goes into an enclosure
containing a 100A/100mA time delayed RCD from which the other CU-West is fed via a distribution circuit of 10mm T+E.
CU-East is a 10way protected by a 30mA RCD, there has never been any nusiance tripping on this half of the property.
CU-West is a 10way split CU protected by two 63A/30mA RCDs.
Having sussed the cause of the nuisance tripping I was in the process of running through my RCD tests to confirm compliance.
Zs at the origin and at CU-East are both good for a TT installation at 3 ohms.
The RCD test results were as expected except the last one.
In summary: 0.5I >1999 notrip / 1I @ 0degs 7.7msecs / 1I @ 180degs 18.2msecs / 5I @ 0degs 4.4msecs (last 3 all
tripped the local RCD) . . . but I5 @ 180degs 8.4msecs but tripped the 100A/100ma RCD at the supply end of the CU.
This overall result was the same for the other RCD in CU-East. All results as expected except the I5 test @ 180degs
tripping the 100A/100mA supply RCD not the local 63A/30mA RCD.
This happened repeatedly and was testing at the CU with all loads off.
I had already done R1 + R2 + Rn and insulation tests on the 10mm T+E feeding the CU-East and these were as expected.
But just to rule it out completely I re-installed one of the CU-East 63A/30mA RCDs next to the 100A/100mA time delayed RCD
via a short length (250mm) of 2.5mm T+E. I repeated the RCD test sequence and exactly the same occurred.
Can anyone suggest what might be going on here or suggest what steps to take next?
PS tester is Megger 1502/2.