Hi all,

Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into account, I have not done any testing for the last 3 years so please be gentle with the below.i feel very rusty.

My neighbour has asked for my help with RCD nuisance tripping. His little brother has temporarily moved into his spare room and brought with him some computer gear. Since then the main RCD has tripped a few times (once in the middle of the night). Finger is firmly pointed at this being the issue.

I have done an earth leakage test on the board. No circuit is causing any more than 2mA of leakage (with all the PC gear turned on).

I tried to test the 30mA AC up front RCD directly with all circuits isolated but it would not trip, it would however trip if I tested from one of the circuits (when energised). My first head scratcher. The trip time was 15mA at x1.

I did attempt to move the upstairs sockets onto the non RCD side of the board as a temporary measure to see if the problem persisted however, as soon as I moved the neutrals to the non RCD neutral bar, it tripped the rcd. My second head scratcher.

I have ran out of time because I needed to take the kids swimming but my thoughts are, the RCD is faulty considering the 15mA trip current. The upstairs RFC which I attempted to move to the non RCD side must be connected to the RCD somehow via a shared neutral or similar.

Would be good to hear your thoughts.

The board is an Volex. RCD is a volex VR63.
 
I tried to test the 30mA AC up front RCD directly with all circuits isolated but it would not trip, it would however trip if I tested from one of the circuits (when energised).
I'm suggesting this because it's a mistake I made once, when I wasn't thinking clearly: Did you test the correct side of the RCD?

I would be carrying out insulation resistance tests first, to rule out any faults in the circuits or equipment. Test L+N to E at 250V, with everything left plugged in/switched on.
 
I'm suggesting this because it's a mistake I made once, when I wasn't thinking clearly: Did you test the correct side of the RCD?

I would be carrying out insulation resistance tests first, to rule out any faults in the circuits or equipment. Test L+N to E at 250V, with everything left plugged in/switched on.
Doh. What a dumbo.
 
Assumption is the mother of all major foul-ups!

Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as circuits are powered on.

An RCD that fails to trip-test on its own is deeply suspicious, but until you have ruled out N-E faults an anything still connected (i.e. it is not really "on its own") there is no point in jumping to that conclusion.
 

Reply to RCD testing issues in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
669

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top